Discuss Smoke alarms for community hall in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

O

Octopus

Hi,

I've been asked if I want to quote for installing fire/smoke/heat alarms in a local community hall which has several rooms and quite a high "domed" ceiling in the main room.

Having not done anything like this before would any members like to give me their thoughts/and/or guidance on such a solution.....


Thanks
 
Hi,

I've been asked if I want to quote for installing fire/smoke/heat alarms in a local community hall which has several rooms and quite a high "domed" ceiling in the main room.

Having not done anything like this before would any members like to give me their thoughts/and/or guidance on such a solution.....


Thanks

Woah!

If it's a community hall - i.e. where public gather to do activities, etc - then it is first and foremost subject to the Regulatory Reform (Fire Safety) Order:2005, and MUST have a current valid fire risk assessment in place.

For you, this means a minimum specification will have been identified and set for any electronic fire detection (as well as for other fire measures, such as extinguishers, blankets, etc.).

Primarily, this means (and is most likely the case) that you will have a document, signed off by an expert (hopefully) who will have defined the grade and category to which the fire detection needs to comply, and to be honest, if this isn't in place, I'd throw it back at whoever asked you, and tell them to comply with the law first - that risk assessment is a LEGAL requirement.

Most likely, and without seeing the property, you'll be looking at a system which needs to comply with BS5839-1:2008. In other words, not smoke detectors in the sense of what you'd install at home. In all probability if the building is only occupied part time, and isn't attached, or posing risk to other premises, the requirement will probably be for an L2 or L3 system design.

Now, you've mentioned high domed ceilings too - those are subject to different spacing rules over the standard spacing set out - normally by reducing the distance by an amount for every so many degrees of pitch the ceiling rises. Any obstruction on the ceiling which is over 10% of the height of the room at any point will also need to be considered.

Given all this - and with all respect, it isn't something you want to "play" with - the penalties for getting it wrong hurt, and include prison if it all goes horribly wrong. Get a professional in to at least design the system (and if necessary carry out the risk assessment) - and play safe. If you're looking for a good fire company in Surrey......by the way :)

As Alarm Man says - collaboration is probably your best bet - get someone with experience..... to at least do the design, and commissioning....and guide you on install if necessary.
 
Hi,

I've been asked if I want to quote for installing fire/smoke/heat alarms in a local community hall which has several rooms and quite a high "domed" ceiling in the main room.

Having not done anything like this before would any members like to give me their thoughts/and/or guidance on such a solution.....


Thanks

Woah!

If it's a community hall - i.e. where public gather to do activities, etc - then it is first and foremost subject to the Regulatory Reform (Fire Safety) Order:2005, and MUST have a current valid fire risk assessment in place.

For you, this means a minimum specification will have been identified and set for any electronic fire detection (as well as for other fire measures, such as extinguishers, blankets, etc.).

Primarily, this means (and is most likely the case) that you will have a document, signed off by an expert (hopefully) who will have defined the grade and category to which the fire detection needs to comply, and to be honest, if this isn't in place, I'd throw it back at whoever asked you, and tell them to comply with the law first - that risk assessment is a LEGAL requirement.

Most likely, and without seeing the property, you'll be looking at a system which needs to comply with BS5839-1:2008. In other words, not smoke detectors in the sense of what you'd install at home. In all probability if the building is only occupied part time, and isn't attached, or posing risk to other premises, the requirement will probably be for an L2 or L3 system design.

Now, you've mentioned high domed ceilings too - those are subject to different spacing rules over the standard spacing set out - normally by reducing the distance by an amount for every so many degrees of pitch the ceiling rises. Any obstruction on the ceiling which is over 10% of the height of the room at any point will also need to be considered.

Given all this - and with all respect, it isn't something you want to "play" with - the penalties for getting it wrong hurt, and include prison if it all goes horribly wrong. Get a professional in to at least design the system (and if necessary carry out the risk assessment) - and play safe. If you're looking for a good fire company in Surrey......by the way :)

As Alarm Man says - collaboration is probably your best bet - get someone with experience..... to at least do the design, and commissioning....and guide you on install if necessary.
 
So how much would it cost to design a system bill??? Rough idea,and do assessment?

Caps off now.

Realistically, risk assessment we do from £250 plus VAT - which is fully BS9999 compliant, and include a written report, fire action plan, and associated material. A typical assessment will take up to four hours on site plus compilation time for the report (plus, it passes some risk in fire safety from you to us).

System design - depends on size and complexity of requirements, number of site visits needed, meetings to attend, design time, and so on - but for a small system such as described above, would be probably around the £200 plus VAT mark - and again, passes risk in design from you to us, which is probably the critical bit, aside from ongoing maintenance records - well, commissioning is important too.

Again - prices are guide, negotiable depending on scope of it all, and a better idea of actual requirements :)
 
Woah!

If it's a community hall - i.e. where public gather to do activities, etc - then it is first and foremost subject to the Regulatory Reform (Fire Safety) Order:2005, and MUST have a current valid fire risk assessment in place.

For you, this means a minimum specification will have been identified and set for any electronic fire detection (as well as for other fire measures, such as extinguishers, blankets, etc.).

Primarily, this means (and is most likely the case) that you will have a document, signed off by an expert (hopefully) who will have defined the grade and category to which the fire detection needs to comply, and to be honest, if this isn't in place, I'd throw it back at whoever asked you, and tell them to comply with the law first - that risk assessment is a LEGAL requirement.

Most likely, and without seeing the property, you'll be looking at a system which needs to comply with BS5839-1:2008. In other words, not smoke detectors in the sense of what you'd install at home. In all probability if the building is only occupied part time, and isn't attached, or posing risk to other premises, the requirement will probably be for an L2 or L3 system design.

Now, you've mentioned high domed ceilings too - those are subject to different spacing rules over the standard spacing set out - normally by reducing the distance by an amount for every so many degrees of pitch the ceiling rises. Any obstruction on the ceiling which is over 10% of the height of the room at any point will also need to be considered.

Given all this - and with all respect, it isn't something you want to "play" with - the penalties for getting it wrong hurt, and include prison if it all goes horribly wrong. Get a professional in to at least design the system (and if necessary carry out the risk assessment) - and play safe. If you're looking for a good fire company in Surrey......by the way :)

As Alarm Man says - collaboration is probably your best bet - get someone with experience..... to at least do the design, and commissioning....and guide you on install if necessary.

Hes Back!!! :)
 
Realistically, risk assessment we do from £250 plus VAT - which is fully BS9999 compliant, and include a written report, fire action plan, and associated material. A typical assessment will take up to four hours on site plus compilation time for the report (plus, it passes some risk in fire safety from you to us).

System design - depends on size and complexity of requirements, number of site visits needed, meetings to attend, design time, and so on - but for a small system such as described above, would be probably around the £200 plus VAT mark - and again, passes risk in design from you to us, which is probably the critical bit, aside from ongoing maintenance records - well, commissioning is important too.

Again - prices are guide, negotiable depending on scope of it all, and a better idea of actual requirements :)

Would you be interested in working with me on this?
 
if ou rang the fire brigade, would they do survey for free...??? i know they can do some stuff

The fire service will not design a fire alarm system or take responsibility for the safety of the building. They will ensure that escape routes are adequate for the flc of people that could be in the building at the time of an evacuation, the amount, type and placement of extinguishers and also the storage of flammable/toxic vapour releasing fumes, fire doors. They do a great job but not to the extent of designing a fire detection system.
 
Ipu makes a good point but not for the purpose of fitting a system. Again the fire service do brilliant work on fire prevention, I have 2 mates in the service and I know what they go through. I have nothing but respect for them.

He does, and they are a great source of advice on a consultant basis - we often get the local brigade involved on more complex work, to ensure they're happy that what we've proposed will meet their expectation.

We also do a fair amount of PN work - and again, talking to the Brigade is always the best solution to getting it lifted fast.

I had a little one not long ago - Grade 2 listed tea room, 300 year old building, no fire detection, no escape planning, various other bits.

Prohibition paperwork stated no trading until full compliance reached - we talked to the SFO, and got that reduced to smoke detectors fitted (radiolink), supply and install four extinguishers, and do the rest on a six month plan. They were open for business again that night.

Just for the record, the Brigade COULD have brought a prosecution on top of the PN - for negligence and failure to comply with the RR(FS)O....it is not the case that they are only prosecuting where injury or death has occurred.

They are an amazing service, more, given how stretched most regions are - and they do still give a great deal of help.
 

Reply to Smoke alarms for community hall in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
316
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Hi all, I'm helping my friend do up an old house he bought a couple months ago and obviously we need to have mains powered smoke detectors...
Replies
3
Views
1K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock