As BS7671 makes no mention of domestic smoke and heat detectors where on the EIC should they go, aside from the old own circuit/ shared with light circuit debate, a discussion with the BCO has prompted this,
Pict
 
Sparkies do not have responsibility for smokes and heats other then providing the cables.....

BUT I think they should be on the EICR.

FYI when I do EICR's I always test smokes and heats and comment on them in the notes...
 
The come under BS5839 Part 6....not debate or conflict with BS7671 or Approved document B.
Domestic smoke if fitted to Grade D (mains/battery backup) can be installed on existing lighting circuit or on there own circuit choice is yours. The form of safe isolation is achieved by the removing the detector from the base using key or tool (screwdriver).
 
As stated they should be certified both to BS 7671 and BS 5839-6. So two certificates should be involved with a smoke alarm installation (or possibly more if multiple Minor Electrical Installation Works Certificates are involved, e.g. with a retrofit installation with radiolink).
 

Reply to Smokes and BS7671 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
315
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
225
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Doing work in a house the other day, and noticed they didn't have any smoke detectors... (well, one.. and it was a small 9v thing) So ive sent in...
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock