I'm hoping someone out there has come across this problem.
Just had -8 days ago- a 6k solar panel system plus 4.8k battery pack installed.
When the electrician left the batteries showed 20%full.
Next few days inverter showed producing 30kwh but batteries did not charge.
We normally use 8.5kwh per day, this was from readings taken off the grid meter over 30 days before installation. I also noticed that overnight, on the meter they installed next to the grid meter, it showed we were exported 0.2kwh to the grid when the solar was not produced.
Contacted the installer but they did not get back to us.
Eventually on the 5th day we had a video call and we noticed that the inverter showed our usage grew and waned in time with the production of solar, more produced more we used.
AHH I know what it is said the installation manager, turn the clamp on the red wire the other way round, it's because you've got an old style fuse box.
I did that and the battery started to fill =success I thought.
However, the battery fills but cannot be used.
If I turn the clamp back to its original position the battery discharges, but the same thing happens. My usage goes sky high and the battery discharges quickly.
I turned the clamp back after it dropped 30%, and that night the grid used 4kwh, the battery wàs full and it sent 3kwh back to the grid.

So now we have a full battery not using it, when the solaris not producing the inverter shows no usage.

We use IKwh from the grid overnight and send 0.2back to the grid overnight

Basically: inverter shows more solar more we use, even when we are only running the fridge and freezer
No solar no power used

Can charge the batteries but they can't he used
Using power from the grid not the batteries and sending to the grid overnight

Only asking here as the company are not getting back to me at all now

Thanks

I have photos but not sure I can upload them
 
put photo/s on desktop. go back into forum, click on attach files, then double click each image.
 
like this:
 

Attachments

  • 003 (2).jpg
    330 KB · Views: 17
First move, get the company back on site…. Second, trading standards…..third, don’t pay them a penny! You can go to your bank and try and cancel payments.
Any fault should be covered by the company’s warranty

region of Scotland? There might be a local member that knows pv that could assist.
 
Last edited by a moderator:
First move, get the company back on site…. Second, trading standards…..third, don’t pay them a penny! You can go to your bank and try and cancel payments.
Any fault should be covered by the company’s warranty

region of Scotland? There might be a local member that knows pv that could assist.
Thank you. We paid a deposit then a part payment after installation. We held back an amount. We are near Perth in Scotland. Thank you
 
Thank you. We paid a deposit then a part payment after installation. We held back an amount. We are near Perth in Scotland. Thank you
Trying to show you what happens when I put on the oven. The display shows that the export to the grid goes up. Problem seems to be that the power usage always corresponds to the solar produced therefore the batteries never kick in
IMG_20210619_091309.jpg
IMG_20210619_104212.jpg

Thank you. We paid a deposit then a part payment after installation. We held back an amount. We are near Perth in Scotland. Thank you
 
Trying to show you what happens when I put on the oven. The display shows that the export to the grid goes up. Problem seems to be that the power usage always corresponds to the solar produced therefore the batteries never kick in
View attachment 86922View attachment 86923
The sun is shining so producing more energy. No appliances being used only fridge freezer same as the first photo. See how our power usage soars in line with the solar produced
IMG_20210619_144555.jpg
 
What make is the invertor and what make is the battery system. There are a number of ways to manage the solar output and battery charge and discharge BUT the arrangement of the clamp meters need to be correct and the battery / invertor system needs to be configured correctly to the arrangement of your clamp meters. I strongly suspect this is not set up correctly.
 
What make is the invertor and what make is the battery system. There are a number of ways to manage the solar output and battery charge and discharge BUT the arrangement of the clamp meters need to be correct and the battery / invertor system needs to be configured correctly to the arrangement of your clamp meters. I strongly suspect this is not set up correctly.
Thank you. The inverter is a Solis and the batteries are Pylontech US2000.
When I did eventually get a phone call, he had me turn the clamp around
 
New posts

Reply to Solar inverter problem? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
798
Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
153
Hi, firstly appologies if my terminology is wrong but I know very little about electrics and have no idea why this is happening - I have 2...
Replies
4
Views
450
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
945
Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock