if you work it out using bs7671 then 4mm is overkill using vd

mV/a/m x ib x L / 1000
2.5 twin is 18mV/a/m

so say 17amps for 4kw say 10m to the inverter

15 x 17a x 10 / 1000 =2.5v which is 1-1.5% depending on supply voltage

now as
where did the 15 come from at the start of that? surely that should be 18 x 16A x 10 / 1000 = 2.88V? which is 1.25% of the nominal voltage.

The problem is, if the supply voltage is coming in at say 251, then that 2.88V will push the inverter over the 253V nominal voltage limit, and with several inverters will cause nuisance tripping on the 10 minute average 253V setting, whereas if it had been 6mm2 the inverter wouldn't be tripping out.

The instant trip settings are up at the 263-264V range, so are reached more rarely, but can be an issue where multiple pv systems are installed on the same transformer

The a.c. cable connecting the inverter(s) to the consumer unit should be sized to minimise voltage
drop
The guidance is to minimise volt drop, I really don't see that 2.5mm2 meets that requirement other than where the inverter is installed at the grid connection point.

1% should be top end, not 1-1.5% is ok in a domestic setting.
 
where did the 15 come from at the start of that? surely that should be 18 x 16A x 10 / 1000 = 2.88V? which is 1.25% of the nominal voltage.

The problem is, if the supply voltage is coming in at say 251, then that 2.88V will push the inverter over the 253V nominal voltage limit, and with several inverters will cause nuisance tripping on the 10 minute average 253V setting, whereas if it had been 6mm2 the inverter wouldn't be tripping out.

The instant trip settings are up at the 263-264V range, so are reached more rarely, but can be an issue where multiple pv systems are installed on the same transformer


The guidance is to minimise volt drop, I really don't see that 2.5mm2 meets that requirement other than where the inverter is installed at the grid connection point.

1% should be top end, not 1-1.5% is ok in a domestic setting.
there are usually multiple settings for each region so you just need to selet the right region for that voltage range if its that close.

done it before and it wont cause nuisance tripping, how can it. a 17amp load on a 20amp+ breaker
 
oh, I see you've changed the distance to make your point valid.

Not sure how many cables you've strung from the CU to the inverter in a loft, but you'll almost always come up short at 7m IME.

besides, the requirement is to minimise the volt drop, not to use the smallest CSA cable you can possibly get away with based on the current carrying capacity.
 
there are usually multiple settings for each region so you just need to selet the right region for that voltage range if its that close.

done it before and it wont cause nuisance tripping, how can it. a 17amp load on a 20amp+ breaker
nuisance tripping of the inverter not the MCB.

so you mean you're not selecting the G83 settings on the inverter? or are you raising the reference voltage from 230 to 240V?

interesting, and likely against the G83 regulations unless you have advance permission from the DNO. But I'd have to ask, why not install the correct cable size in the first place?
 
Last edited:

Reply to Solar PV wages in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a 6kw PV with a 6kw Growatt battery and invertor. I have a solar iboost going to the hotwater tank. Recently I had a Ohme Home Pro...
Replies
2
Views
2K
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
1
Views
438
Hi, Recently I had solar panels fitted and realised how they have done it and I hope someone will be able to give me advice how bad and dangrous...
Replies
16
Views
4K
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
408
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
423

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock