In my opinion if you have distribution boards downstream a reasonable distance from the other distribution boards then these really should have their own SPD as well. One at the origin won't cut it.
When a sub-distribution board is located more than 10m away from the mains SPD, additional SPDs are required.
Both his consumer units are close together.
It leaves the question of does the garage need one.
 
Last edited:
Could someone kindly share why the SPD unit must be in parallel? I'm confused sorry! Hard to say without a basic wiring diagram of the current installation.
I assume a plastic 100A isolator switch with a built in SPD would work straight after the main supply incoming tails. Then anything downstream will be protected, including the time delayed RCD and all the other CCUs. . Though not strictly allowed (dno only), but could be placed in the meter cabinet. Here are examples:

Wylex type 2 SPD isolator, suitable for TT


There may already be an isolator after the main tails not sure. But that could be replaced with this.
 
Last edited:

Reply to Spds - multiple consumer units in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
519
hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
238
Evening all . Just a quick question what do you guys typically charge for an rcbo spd consumer unit change 14 way . 10/11 rcbos few spare ways ...
Replies
25
Views
3K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock