I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N & E. Typically they plug into a holder, sometimes as two separate SPDs (e.g. Hager, with separate E connections), more often now as one combined SPD (e.g. Fusebox) with one each of L, N & E connections.

For a TN-C-S supply where N & E are typically connected a very short distance way (e.g. well under 3m), can someone tell me why the SPD across N & E is actually needed?

I can see the merit for TT and maybe TN-S supplies, and wonder is it just to simplify making only one devices that will serve all applications?

Do single module Type 2 SPDs for use across just L & E actually exist?
 
Good question. At a guess, I'd say the voltage drop between the SPD and the N-E connection at the cutout could be significant. So there could be a potential difference between N and E within the installation.
 
Do single module Type 2 SPDs for use across just L & E actually exist?
Yes, for example:

However, the reality is the L-N-E style are far more useful in general as they can be used for all style of earthing (as the risk of L shorting via N to E is negligible for TT use) and it reduces the need to worry about the inductance of the cabling from, for example, the N-E joint in a TN-C-S system to the point where the SPD is fitted.

As you need to keep the inductance down for the very high dI/dt of a lightning surge, and so total loop distance from L via SPD to N/E to no more than 1m and ideally less than 0.5m, you can only usefully deploy a single module SPD if the cutout is very close to the CU or similar where the SPD is fitted.
 

Reply to Surge protection devices for PME supplies? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
510
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock