I’ve been avoiding posting any of my drawings here.

Basic03_zps3aaa6535.jpg

I knew I hadn't quite grasped the point of distinction Tony. The two live wires are IN PHASE (they are driven by the same winding and reach their maximum values simultaneously) but of OPPOSITE POLARITY (the center tap means that relative to earth one will be +ve and the other -ve). Have I got it?
 
I knew I hadn't quite grasped the point of distinction Tony. The two live wires are IN PHASE (they are driven by the same winding and reach their maximum values simultaneously) but of OPPOSITE POLARITY (the center tap means that relative to earth one will be +ve and the other -ve). Have I got it?

Yes you have it, two sine waves, both pass through 0 at the same time, the polarity is 180 degrees out of phase.

If you look on a oscillascope you would see the positive of one sine reach its maximum at teh same time as the other meets its negative max. The two sine ways give you the voltage. If they were in phase the two sine ways would be superimposed, the area of the sine would not change.

Cheers
 
I knew I hadn't quite grasped the point of distinction Tony. The two live wires are IN PHASE (they are driven by the same winding and reach their maximum values simultaneously) but of OPPOSITE POLARITY (the center tap means that relative to earth one will be +ve and the other -ve). Have I got it?

Yes that is correct, if you looked on a oscillascope you would see the two sinewaves, the positive of one meets its maximum at the same time the other sine meets its maximum negative.

Cheers
 
Do we need to consider the HV/LV displacement of a Tx to understand what voltage and current will exist in a LV polyphase system?


Cheers

Yes, the primary makes a difference to phase shift for poly phase transformers. I’ve written an article about all kinds of transformers on another site.

The commonest type of 3 phase unit is vector group Dyn11 where the secondary leads the primary by 30°. The 11 comes from the clock position.
Vector groups are based on the physical angle not the output waveform. Hence the centre tapped being 0°.
 
Yes, the primary makes a difference to phase shift for poly phase transformers. I’ve written an article about all kinds of transformers on another site.

The commonest type of 3 phase unit is vector group Dyn11 where the secondary leads the primary by 30°. The 11 comes from the clock position.
Vector groups are based on the physical angle not the output waveform. Hence the centre tapped being 0°.

Hi Tony

Out of intrest, your diagram uses kirchoffs cxurrent law to determine the neutral current, im not aware of the having to condider the primary/secondary winding connections, equally when calculating voltages within the LV system i have never taken winding displacments into account.

Could you explain how you take into account the phase displacment in your calculations.

Paralell Tx require phasing(circulating currents), and 30 degree phase shift nulifies third harmonics, im interested into how your calculations include primary/secondary phase displacement.

Cheers
 
Yes you have it, two sine waves, both pass through 0 at the same time, the polarity is 180 degrees out of phase.

If you look on a oscillascope you would see the positive of one sine reach its maximum at teh same time as the other meets its negative max. The two sine ways give you the voltage. If they were in phase the two sine ways would be superimposed, the area of the sine would not change.

Cheers

To play devils advocate, what do you get if you place the oscilloscope on L[SUB]1[/SUB]→L[SUB]2[/SUB]?
 

Reply to Split phase in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
570
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
931
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock