Discuss Spurs off Spurs on radial circuit in the Industrial Electricians' Talk area at ElectriciansForums.net

S

stratplus

So you can spur off Spurs on a radial socket circuit, is this because the cable is protected via a 20amp breaker at the board compared to 32amp on a ring?
 
Think about the current carrying capacity of the cable. Are you a trainee ?
I am a trainee yes Andy.
Been trying to get my head round rings/Spurs and radials/Spurs. I can understand if you spur off a ring that piece of cable can take potentially 26amps (two 13amp fuses). Now if you spur off that spur your current could be 52amps so overloading the cable.
Finding it difficult to understand how with a radial you can spur off spurs without overloading the cable.
 
I am a trainee yes Andy.
Been trying to get my head round rings/Spurs and radials/Spurs. I can understand if you spur off a ring that piece of cable can take potentially 26amps (two 13amp fuses). Now if you spur off that spur your current could be 52amps so overloading the cable.
Finding it difficult to understand how with a radial you can spur off spurs without overloading the cable.


Radials usually covered by a 20amp breaker, cant see by extending the radial how you would overload the cable Appendix 15 BYB
 
Last edited:
I am a trainee yes Andy.
Been trying to get my head round rings/Spurs and radials/Spurs. I can understand if you spur off a ring that piece of cable can take potentially 26amps (two 13amp fuses). Now if you spur off that spur your current could be 52amps so overloading the cable.
Finding it difficult to understand how with a radial you can spur off spurs without overloading the cable.

Well you said it yourself in your opening post. The OCPD is 20A which is less than the CCC of the cable. With a ring circuit the standard OCPD is 32A which is higher than the CCC of the cable in that leg and therefore the potential loading must not exceed that of the CCC of the cable.

See appx 4 for cable calculation procedure and appx 15 for standard circuit arrangements as your revision points for this.
 
Well you said it yourself in your opening post. The OCPD is 20A which is less than the CCC of the cable. With a ring circuit the standard OCPD is 32A which is higher than the CCC of the cable in that leg and therefore the potential loading must not exceed that of the CCC of the cable.

See appx 4 for cable calculation procedure and appx 15 for standard circuit arrangements as your revision points for this.
Ok, thank you Andy. Got it now. Every time I read and think I understand something, I read something else and have another ten questions! Read the same four pages for 2 months to understand lighting circuits!
 
Pete what do you mean by "can't see by extend"?

If you are adding a new socket to a radial you are either extending the circuit, I'll clarify, by extending the radial, I assume you are adding a socket from the last point on the radial.
Read Appendix 15 BYB and get back to us if you don't understand anything.
 
Last edited:
Before spurring from a RFC or a radial you must work out what is on that circuit now, what will be on it afterwards and can the cable/protective device provide adequate distribution and protection?
 
If you are adding a new socket to a radial you are either extending the circuit, I'll clarify, by extending the radial, I assume you are adding a socket from the last point on the radial.
Read Appendix 15 BYB and get back to us if you don't understand anything.
Hi Pete, not doing any electrical work just trying to understand the circuits.
Ok I understand that if you are adding a socket to the end of a radial you are extending. I was more thinking about a spur from a socket so you'd already have two cables in there, spurring would be adding a third cable.
 
Hi Pete, not doing any electrical work just trying to understand the circuits.
Ok I understand that if you are adding a socket to the end of a radial you are extending. I was more thinking about a spur from a socket so you'd already have two cables in there, spurring would be adding a third cable.

Nothing wrong with that, have you had a look at the BYB yet?
 
There is a dedicated trainee forum here that you could join if you are in training.

Thanks Andy but I dont think stratplus is a Trainee after reading through his threads over the past 3 years. Working sparky that dose not understand basic spurring? (appendix 15 btw, last page before the index).


May I suggest that members do not give a step by step guide, only positive prompting towards learning what he installs.
 
Thanks Andy but I dont think stratplus is a Trainee after reading through his threads over the past 3 years. Working sparky that dose not understand basic spurring? (appendix 15 btw, last page before the index).


May I suggest that members do not give a step by step guide, only positive prompting towards learning what he installs.
Did my 2330 some years ago, I'm not a sparky. Electrics is something I have been interested in for a while but have no intention of doing electrical work outside of my own home. Just because I did my 2330 (NOT an nvq) doesn't make me a competent spark.
I am constantly coming back to reading my books to help my understanding.
 
Thanks Andy but I dont think stratplus is a Trainee after reading through his threads over the past 3 years. Working sparky that dose not understand basic spurring? (appendix 15 btw, last page before the index).


May I suggest that members do not give a step by step guide, only positive prompting towards learning what he installs.
College evening class practical consisted of wiring certain circuits on a board and working through them as quickly as you could because you only had a couple of weeks (at two evenings a week) to complete the practical assignments. That was the easy bit. It's only later when you sit down and think about the circuits that you realise how little you REALLY understood. That's something I'm now trying to rectify.
 
College evening class practical consisted of wiring certain circuits on a board and working through them as quickly as you could because you only had a couple of weeks (at two evenings a week) to complete the practical assignments. That was the easy bit. It's only later when you sit down and think about the circuits that you realise how little you REALLY understood. That's something I'm now trying to rectify.


Whilst you typed the above I sent you a PM. Everything is cool and I hope my explanation of spurring is a benefit to you.
 

Reply to Spurs off Spurs on radial circuit in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi guys, super basic question: For a room layout like this, with my understanding that a lighting circuit downlight radial goes from one point to...
Replies
2
Views
347
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hi! I've got a couple of 32A Wago clips. Creating a spur socket from a ring circuit with these is quite easy, but I wanted to know if it's...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock