S

sparkydude

Hi All, just after a bit of advice with regards to using the following staircase timer from theben.

ELPA 7

Just need to confirm that i can wire it with two cores in parallel with no indicator lamps fitted.

It is to be used in a hospital corridor to override the timeclock when its dark inside and the photocell is holding off as the light cell outside says its still bright.

Basically just need to push retractuve switch , switch operates staircase timer set to 20 minutes then after 20 mins , goes off.

Could someone have a butchers at the diagrams as they seem to say 3 or 4 wire operation , but does not show my particular set up.

ANy help appreciated

Nick
 
Hi Sparkydude

Can't magnify your picture enough to see the connections, should imagine it needs L-N to it, if the other two are the switch connections then yes it would be OK to parallel the time switch connections to overide.
 
I take your original post to mean that you want to use this timer to override the time switch, if that is the case then you need a switch live, a switch wire and a neutral at this unit, don't understand which switch you only have two wires at, you want to use the slide switch on the unit to bring on your lighting for 20 minutes yes?
 
No , idea is to have retractive switches in the field to enable the client to power the lights up for 20minutes if they feel the need. so the push to make switches have only 2 cores at them


Hope this is clearer


Nick
 
hi guys, just a quick question while use r on the subject.

first off ill be changing a broken existing timer (no labelling diagram) that is knackered and will be replacing it with same timer ur discussing above when i upgrade a fuse board this weekend.

correct me if im wrong:
L: incoming
N: incoming
3: load (light fittings feed)
L+4: switching cable operating push switches (N/o) in parallel on each floor with on/off light switch on bottom of staircase acting as override to turn off or on permanently during opening hours (office building), would this work on timer mode and stay on permanently if need be as long as contact is closed ie light switch on ground floor permanently in 'on' position.

any help would be appreciated!
 
Hi Jay.

Yes your connections are right for the staircase switches and lights, but for an override function you would need to connect your switch to terminals 1 and 3 in the timer.

You ask "would this work on timer mode AND stay on permanently" not sure what you mean by that, the timer mode is activated by the staircase switches, maximum 'on' 20 min. but once the timer is overridden by the normal light switch, the lights would be permanently on.
 

Reply to Staircase Lighting Timer in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi All, Thankyou in advance for your help I have a block of 5 stories with a staircase timer already installed in a 3 wire connection setup. I...
Replies
2
Views
925
Hi I replaced a Flash immersion timer with an apt one today and it seemed straightforward but just wondering should the light on isolation switch...
Replies
5
Views
440
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
620
I have replaced a staircase timer because the previous one was fault. There was a problem the light stayed on all the time. When i replaced the...
Replies
3
Views
856
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
975

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock