mark123

Hope someone can help, Basically i'm just getting into heavy industrial and when i have been opening various panel's and motors i can't get my head around the actual terminating of star,delta from the panel to the motor as they seem to move L1,L2,L3 to L2,L3,L1. Any ideas?
 
Hi delta connection is U1 TO V2 V1 TO W2 W1 TO U2
or as you have L1 TO L2 L2 TO L3 L3 TO L1 Hope this helps sorry don't know how to insert a diagram have a look at this site it might help Patchn - Home
 
stardelta.jpg



Star Delta can be a little confusing, so you're not alone. I know sparks who won't even touch it!

stardelta3.jpg



The above image is of alternative wiring. Note at the delta contactor that the phases swap.

Basically you have to follow the wiring from the supply side of the line contactor, through the motor windings and back through the delta contactor back to the supply, so that you start at one phase and end at another.

One other thing:

Overloads; if before the line contacor and delta contactor, as in a motor breaker, set at 100% of motor's flc (full load current)

If after the line contactor then set at 58% flc

Another tip: setting the star to delta transistion time. Clamp a phase with an ammeter. Start the motor in star and watch the current rapidly rise then settle for a second. Once the motor has started the current will rapidly fall. Its at this point that, nearing the end of the fall, that the timer should switch over to delta. If the timer is set too short ie. before the current falls then the overload or motor breaker will trip! High inertia loads, such as fans / flywheels, will take longer to start up so the timer may be well in excess of 10 secs.

Regards
Richie
 
Last edited by a moderator:
Don't you just swap two connections over, from the same set of wires ie U1, V1 etc at the motor.
 
Last edited by a moderator:

Reply to Star Delta connections regarding motors in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock