Hi, I'm a newbie here and I need help with starting some 2 pole 20KW motors, can I still use the normal 22KW DOL starters or is it better to upgrade the starters because of the larger starting current - any advice would be gratefully received, Thanks kjwudsph
 
A 22 kW DOL starter would be quite a design. I've never seen DOL starters used above 7.5kW to be honest, the start current would be extremely high and prolonged and the starting torque would be very low especially with a 2-pole motor.

Why not a star-delta starter or even a soft starter/ VFD?
 
I have 37.5Kw starting DOL ... Old Russian lathes.... its your supply that denotes the need for restricted starting currents having said that a motor 4kw or higher really wants to be looking at some form of soft starting if its on a 100amp incoming supply as they can give excessive mains transients while starting up and the DNO look dimly on such issues.
 
And it also depends on the load the motor is driving, the number of starts per hour, the motor design etc. If the motor starts a low-inertia load infrequently and the supply is large enough, you can get away with it, however a full understanding of the operating conditions is needed to give any useful advice on this.
 
Too right Nunes had a firm call me out who had DNO come down hard on them found they were inching 30kw motors and dipping the whole neighbourhood - a nice little Inverter install for me :)
 
In the days before inverters sounds like it would have been a job for a geared down pony motor. Or else, Klunk-Klonk. Klunk-Klonk. Klunk-klonk, the sound of 80A contactors wearing out quickly.
 
You nailed it the contactor had recently been changed for that very reason ....klunk klunk klunk klunk then RUN .... grrrrrr Trip blown contact points phase out. It had already had a replacement contactor only 2months prior to me going out to it.
 

Reply to Starting 2 pole motors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
662
We are in the process of restoring 4 of a group of 5 Brookhirst DC motor starters from 1936. These are a thing of beauty and the engineering in...
Replies
1
Views
1K
Hi all I have a small DC motor that I pulled off from an ABS car module and need help identifying some parts in order to hopefully rebuild it. 1...
Replies
10
Views
1K
Hi all Back in July last year I installed a new pool pump/motor. The problem is it's now making a humming noise and trips the breaker. I...
Replies
21
Views
2K
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock