Discuss Steel Tape Armour and Reduced Neutrals in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table so that I can check the figures.

Secondly, correct me if I am wrong but 3ph with a reduced neutral should only be used on a balanced load ie a single pump/motor etc - it is not meant to be used to feed a panel supplying single phase loads?
 
It'll be down to the Manufacturer as to what specification the armour is designed for and whether or not it has a BASEC standard. I'd have thought the biggest pain would be getting the correct glands for it.

As for the reduced size Neutral see 524. The dependant factors are on line conductor size / type and not useage.
 
After a bit of research it does look like Americans / Canadian sparks are allowed to use the steel Tape as the ground on some of the cables but not on the all. It has to be specifically rated so you can use the steel tape wrap for the grouding.

So as above I would want to check with the cable makers insctructions and specification manual ( very carefully ) before committing to this type of cable in a UK install
 
Steel tape cables were not unusual in this country, normally covered with tar soaked hessian. Where have they ordered it from as I have not seen it in modern use?
 
I would be concerned that the resistance / heating is much higher as it is spiralled around. Also if the usual glands would properly grip it to connect.

Maybe they have considered that already, but it is not something i have seen on any modern power cable, just sometimes the armour on fibre networking stuff where it is largely mechanical protection.
 
As westwood says, hessian/tar jobs.
This is a house supply, originally 3 phase, I think from the 1930's. The hessian has rotted but the steel wrap can be seen where the cable comes through the wall. You would think that the steel would be rusted and knackered but it is solid as a rock. The head had to be sorted out by ENWL so they had to cut some of the steel spiral back...with amazing difficulty, to re do the cable head and re earth with a constant force spring.
These days, I can't imagine it being anything like as solid.

IMG_2170.jpg
 
I would be concerned that the resistance / heating is much higher as it is spiralled around. Also if the usual glands would properly grip it to connect.

Maybe they have considered that already, but it is not something i have seen on any modern power cable, just sometimes the armour on fibre networking stuff where it is largely mechanical protection.
Agreed, forgot about the ambient temperature, I am working in Sinai on a base to UK regs where the temp is usually 30C to 40C, so overheating would be a problem too. Its 3 x 120mm phase and 70mm neutral with no earth, but the tape looks so thin and its been supplied to be used on the new barrack blocks - these have single phase loads which are by no means balanced - yes if everything is on at the same time its ok but not everyone puts the kettle or AC on at the same time.
 
I would be concerned that the resistance / heating is much higher as it is spiralled around. Also if the usual glands would properly grip it to connect.

Maybe they have considered that already, but it is not something i have seen on any modern power cable, just sometimes the armour on fibre networking stuff where it is largely mechanical protection.
I do not think so, rather someone has seen that this cable is cheaper than what was ordered and thought to save some money. Yes Steel Tape needs its own set of glands and terminating is a pain (cut fingers etc). I have said that if they insist on using it then it has to be derated down to the same size as the neutral and an external earth ran with it.
 

Reply to Steel Tape Armour and Reduced Neutrals in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
613
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
349
https://gadsolutions.biz/regulations/swa-as-the-cpc Anyone know how reliable the tables on this website are for determining whether the armouring...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock