Any suggestions as to possible causes of RCD tripping in the below domestic scenario would be helpful:

Origin:
single phase TT supply into an external cabinet housing cutout and our installed 100A 100mA Type S 2Pole RCD. Earth Rod has also been sunk here.

House:
3c SWA supply to house from above to a TP&N board with single phasing kit. All circuits from this board are on 30mA RCBO’s.

We have been turning circuits on once tested over the course of last 2 weeks and the board has sat with all but 2 circuits on for nearly a week without issue but all of a sudden today we have had nuisance tripping at the RCD in the cabinet.

We have insulation tested the sub-mains again as a result of this and everything seems fine. So at the minute I’m unable to find the cause, none of the RCBO’s have tripped at any point.

Any suggestions?
 
I reckon it'll be a neutral to earth fault on one of the final circuits, I've know this phenomenon to be undetected by RCBOs, tricky to explain exactly why though.
 
Sometimes in particular TT systems a neutral to earth fault may not cause sufficient imbalance due to the neutral path having lower resistance than the path to earth. So you could have a dead short neutral/earth fault but the majority of current flow stays with the neutral path which may not create sufficient imbalance to trip the device.
 
Thanks Westward, saved me the effort. Also why if you snip a 'dead' cable on a TNCS or TNS system the relevant RCD will generally 'trip' often resulting in explaining to a customer that you're not an idiot and you haven't cut a live cable. But 9 times out of 10 you'll get away with it on a TT.
 
Sometimes in particular TT systems a neutral to earth fault may not cause sufficient imbalance due to the neutral path having lower resistance than the path to earth. So you could have a dead short neutral/earth fault but the majority of current flow stays with the neutral path which may not create sufficient imbalance to trip the device.

an S type?

Not totally convinced BUT it could be accumlated leakage ....... especially with RCBO's ........

Wonder if the OP has an earth clamp leakage meter?
 
Thanks, most of the above makes sense to be honest - you do in fact get away with it on TT majority of time in like you say.

However why doesn’t the RCBO trip ahead of the time delayed?
 
Thanks Westward, saved me the effort. Also why if you snip a 'dead' cable on a TNCS or TNS system the relevant RCD will generally 'trip' often resulting in explaining to a customer that you're not an idiot and you haven't cut a live cable. But 9 times out of 10 you'll get away with it on a TT.
You need to ditch the neutral or you provide an alternative path for the neutrals of all the circuits still in use.
 
Most obvious to me would be leakage current not enough on each circuit to trip 30mA RCBO but accumulatively unless the 100mA is tripping out much lower than it should.

I’ve thought about trying a 300mA - there’s over 20 Rcbo’s

I haven’t ramp tested but I have had 2 different manufactured RCD’s in today, both tripping
 
You say it's been ok for 2 weeks, then the nuisance tripping has started. You also mention the cabinet with the 100mA RCD is external. Is this tripping happening at the same time of day/night? Have the atmospheric conditions changed? I'm wondering if the cause may be condensation related.
 
You say it's been ok for 2 weeks, then the nuisance tripping has started. You also mention the cabinet with the 100mA RCD is external. Is this tripping happening at the same time of day/night? Have the atmospheric conditions changed? I'm wondering if the cause may be condensation related.

It could be something as simple as this Tony
 
Re OP's #1: Which two final circuits?

You mention a TN&N board converted to SP. How many final circuits are there?

Suggestions:

Test the IR of electric ovens, hot wire element electric hobs, washing machines and tumble dryers and dishwashers, immersion heater.

Take a close look inside any outside light fittings and switches.

Pour 2-3 gallons of water around the earth electrode.

Check tightness and solidity of all connections.

Carefully remove sockets and look behind them for securing screws close to live conductors.
 
Hi - Agree Murdoch and Strima I would not change out 100mA S type without a test result showing it's at fault. As others have said, it's quite likely a N-E fault exists. If it's in a final circuit unfortunately the single pole rcbo won't remove it from play.
Some questions and thoughts -
What parts of this installation are new?
Any patterns to the tripping?
What is the site Ze? Locate the rod and confirm the impedance of connection from rod to MET and CU earth bar with wander lead. Repair if required.
How long is the underground SWA linking cabinet to CU? What protects this cable? What were the cable IR results please? Carefully check all connections from cutout to CU and the polarity.
Happy Hunting :)
 
I agree with the earth leakage clamp approach to see where the leakage is coming from. Could be cumulative across that many final circuits, without tripping individual RCBOs. I've seen 'normal' leakage on a 7-way board cause a 30mA incomer to nuisance trip, so it's feasible that all your final circuits could do the same to a 100mA. Unlikely, but feasible.

One last thought - I fitted a Lewden (aka Control Gear) 100A 100mA type S a few years ago and kept getting called back for nuisance tripping, when the 30mA downstream never batted an eyelid. All IR tests >99M. I replaced it with an MK type S and never been a problem since. Funnily enough I don't use Lewden RCDs anymore!
 

Reply to Strange RCD tripping scenario in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
402
At my place of work we have just had multiple LED advertisement screens fitted outdoors, the company specified 16amp RCBO’s for each set of...
Replies
19
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
870

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock