During a recent EICR the RCBO keeps tripping , i measure leakage of 2.6 ma when clamped around line and neutral, when i clamp the cpc i get over 10 ma ,its a PME supply 0.09 ZE.

These RCBOs have a functional earth , the RCBO ramp tested at 21 ma .

does anyone have any idea why this is happening ? And how to solve it?

D2B81727-A72D-4321-98D8-237471E93657.jpegFD387FFC-89F8-458C-B0D7-549FD304049D.jpeg
 
Ir reads 199 Megs minimum ,there are 4 lamp post so I have removed local fuses to try to track this down.
the cpc current is present even when the main switch is off,but its in flats communal area where all flats are supplied by a ryefield
 
May I have a little more detail please?

a. A sketch of the wiring of the final circuit for the street lamps and could you measure the neutral to earth voltage at the board where is the rcbo.
b. A picture and drawing of how the lamps are connected to their feed including how the lamp metal work is connected to terra firma/earth and the feed armouring and cpc terminations.
c. If the lamp posts are connected to an earth rod what are the currents in the 4 earth conductors please?
 
The CPC current could be anything, basically street furniture will be an earth rod of some form so any voltage seen at the MET due to currents on the PEN will cause some current to flow.

If the usual leakage is small as it is here then probably there is an intermittent event causing it, say water getting in to a easy-drained junction box or similar. Another cause for RCD tripping can be a rapid change in voltage due to something else kicking in, but usually it needs to be a lot of current suddenly to get a high enough dV/dt to push a troublesome amount of current through the capacitance.

2.6mA works out at about 36nF at 230V, which is probably around 100m of SWA cable at a rough guess. Is that anywhere close to what you see?
 
Fairly common with cheap LED lamp drivers, to make life easy, connect non LED lamp and see does it happen. then check your reading again, if they are clear and the RCBO doesn't trip then you know the LED driver is the problem.
You will only drive yourself around the bend
 

Reply to Strange Residual Current Device tripping on lamp post in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
There are 2 inverters feeding into a dorman smith C16 rcbo , every time I visit this site (communal area power) it has tripped. it switches on...
Replies
13
Views
2K
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
Replies
25
Views
6K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock