My guess without looking up the figures and doing the maths myself is that if it's legit it's probably down to still being able meet disconnection times based on a very low Ze? I'm assuming it's a 90C+ rated cable type.
 
Seems a long run,& on 80 amps.
Wonder what the actual design current is.
Some cable types on the right method are comfortably into three figures on 16mm so it's not impossible (but I'll grant you unlikely!)
 
Sound like someone just looked at the fuse and current-carrying capacity and nievely said "yes gov, that will do".

Plugging in 80A, 125m and a generous 5% drop in to the Doncaster cable calculator suggests 50mm cable...
 
Maybe they don't need 80A, but I really doubt that fuse would meet Zs disconnection at that length. Also if they only needed, say, 40A or so then fusing down to that (or just above) would achieve selectivity with the (presumably) 100A cut-out supply fuse.
 

Reply to Sub main 125m in16mm with 80A 1361 over current device in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
645
At long last my wife is getting her new kitchen and the contractor will be running 10 or so new circuits from a new sub panel. The sub panel...
Replies
1
Views
825
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
555

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock