Discuss Sub-mains needed? in the UK Electrical Forum area at ElectriciansForums.net

L

Lionscourt

I was looking at a job today and ran across the following: 2-year old installation, 100 amp main fuse, Henley block next to the meter, with the main tails in and then out to the house. Along with this are three sets of 16mm SWA coming out of the Henley block (neutral and earth wires not properly colour coded) going off to various out-buildings. One of the cables goes to a garage with a full 17th edition board (there's a games room above, and a hot tub outside - it's a very nice garage). The owner wants some work done in this location.

Am I right that a sub-mains needs to be installed at the meter, with a maximum fuse size of 80 amps, and that I need to insist on this before I do any work?
 
The way it is at present means the SWAs are not fused or RCD protected! Think of the CCC of 16mm SWA and then think they are only 'protected' by the 100a main fuse! Definately needs a secondary CU adding with appropriate MCBs, creating proper distribution circuits.
 
Thanks for all your replies, I appreciate it. The cables come directly into the meter box, which is a standard plastic exterior wall box. They are not glanded at that end - the armouring is simply cut off a few inches into the box. The one cable whose other end I saw in the garage was glanded at the consumer unit.

There's obviously no room in the meter box for the Wylex isolators suggested by somersetsparks. The only thing I can think of that might fit in there is an MEM 800KMF, though I couldn't gland to that. Should the owner want all three cables properly fused I'm not sure 3 of those could even be squeezed in, or whether it's legal to do so.

I spoke to Napit tech support and they said I'd by okay to add a circuit to the existing garage unit as long as I wasn't making the installation less safe, but that I should recommend to the owner that the supply cable be fused at the meter end.

So, assuming the owner wants the extra work done:

Does the cable need a gland at the meter box, assuming it is properly earthed at the other end?

Can any necessary fuse units go in the meter box, assuming there is room for them?

I'm back there on Thursday so I'll see what happens when I explain this all to the owner.
 
Thanks for all your replies, I appreciate it. The cables come directly into the meter box, which is a standard plastic exterior wall box. They are not glanded at that end - the armouring is simply cut off a few inches into the box. That needs to be sorted and the SWA given mechanical protection as afforded with glands

The one cable whose other end I saw in the garage was glanded at the consumer unit.

There's obviously no room in the meter box for the Wylex isolators suggested by somersetsparks. The only thing I can think of that might fit in there is an MEM 800KMF, though I couldn't gland to that. Should the owner want all three cables properly fused I'm not sure 3 of those could even be squeezed in, or whether it's legal to do so.

I spoke to Napit tech support and they said I'd by okay to add a circuit to the existing garage unit as long as I wasn't making the installation less safe, but that I should recommend to the owner that the supply cable be fused at the meter end.

So, assuming the owner wants the extra work done:

Does the cable need a gland at the meter box, assuming it is properly earthed at the other end? See my reply above yes you should gland both ends

Can any necessary fuse units go in the meter box, assuming there is room for them? If there is no room in the meter box, and i'm assuming this is the outside type of box, just gewt a suitable metal clad lockable IP enclosure and piggy back it next to the meter box . Fit all the switch gear into , gland the SWA into it as well.

I'm back there on Thursday so I'll see what happens when I explain this all to the owner.

.....................................................
 
I'd second malcolms point about a seperate enclosure, With the smart meters coming soon, they may make the customer have any equipment moved to fit their new meter in, after all no customers equipment should really be mounted in the meter box, especially not 3x switch Fuses, or even 3 x KMF's.
 

Reply to Sub-mains needed? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
338
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
758
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
893

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock