Discuss Submain on a TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Not too difficult to achieve, if you know what you're doing!! The problem in the UK, is this almost total acceptance of the crazy numbty 200 ohms as mentioned in BS7671 and OSG's as being the value to aim for!!

Never even mentioned the 200 ohm bull, but in all honesty, do you think that on this job, the value of Ra is going to be low?

I don't somehow
 
If that was the case then no 5 secs is fine but not come across a TT system with a low Ra yet. But I'll keep looking


I know of more than just a few domestic TT systems in Essex, that are below 1 ohm, and in some cases, with better than the local towns DNO TN-S values!! Commercial and/or industrial made roded ground fields, are very rarely in excess of 1 ohm... As i said the biggest problem in the UK is this numbty 200 ohm malarkey and using thin twigs for earth electrodes. I'd never even heard of them before coming on UK electrical forums, and still to this day, haven't seen one in the flesh so to speak!! Only relatively recently have i seen a 1.2m 5/8'' rod, i'm used to seeing and using 2.4m and 3.2m rods.... lol!!
 

Reply to Submain on a TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
899
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock