Discuss Submain swa size check in the UK Electrical Forum area at ElectriciansForums.net

bigspark17

-
Arms
Reaction score
718
Just after a bit of advice from thoose of you that deal with this regularly & want to make sure i get it right.

Swa submain to phone network mast
63Amp single phase supply
Pme supply assumed ze of 0.35
245M run

Ive been trying to calculate which size swa & cpc or 3c swa to go for, would like any experienced input.
Thanks
 
What is your protective device ?
Fuse, mccb , mcb etc?
Also installation method
May restrict your calculations as your max zs will hinder you as I would imagine your ze will probably be less than 0.35
As an example a type c 63 amp mcb has a max zs of 0.34 ohms without your 80% rule of thumb.
 
What is your protective device ?
Fuse, mccb , mcb etc?
Also installation method
May restrict your calculations as your max zs will hinder you as I would imagine your ze will probably be less than 0.35
As an example a type c 63 amp mcb has a max zs of 0.34 ohms without your 80% rule of thumb.

I was going to install switch fuse 63amp bs88.. install method is buried in ground with warning tape buried above.

Ze is a major factor. Any chance you can site survey and measure it?

Unfortunatly not as the DNO have not installed the supply into the customer built hut yet, :/
 
IMG_2041.PNG
 
Very rough calculation whilst sat on my sun lounger next to the pool.....If the earth leakage relay was set to o.8xIn then 50V/50A=1 Ohm

Gives you a bit of room to play with if your taking Ze at 0.35 Ohms.

If your calculations are using 63A as Iz then i recon your looking at using around 150mm based on volt drop.
 
The DNO will be able to tell you the designed Ze for the supply, if it is a completely new supply then they will possibly be working to a maximum value of 0.25 in their calculations.
0.35 is the stated value for existing networks.

Assuming this is a 100A supply coming in that is, if it's bigger than that then the Ze requirements are lower.
 
Very rough calculation whilst sat on my sun lounger next to the pool.....If the earth leakage relay was set to o.8xIn then 50V/50A=1 Ohm

Gives you a bit of room to play with if your taking Ze at 0.35 Ohms.

If your calculations are using 63A as Iz then i recon your looking at using around 150mm based on volt drop.

Can you get an earth leakage trip with a 50A tripping current? I've never yet seen them go above 10A

What are you basing your VD calculation on?
My rough calculations based on voltage drop come out at 2x50mm in parallel, based on a mobile phone mast not including any lighting requirements and not having any specified voltage limits stricter than 6%
 
Can you get an earth leakage trip with a 50A tripping current? I've never yet seen them go above 10A

What are you basing your VD calculation on?
My rough calculations based on voltage drop come out at 2x50mm in parallel, based on a mobile phone mast not including any lighting requirements and not having any specified voltage limits stricter than 6%
I got the mV/A/m figure from a manufacturers data sheet. Good point about to 50A setting....I just assumed they did. I've fitted one with a 30A max setting before.
 
Thanks for replies.. some good input from respected members.

Its the max disconnection time & VD that are the main influences over this length.

I was looking at putting a kmf or switch fuse between dno and metering with a bs88 gG 63amp fuse in, @ 80% value gives me a max zs of 0.62.

Using 95mm 2c swa & 35mm cpc gives me a max Zs of 0.56 assuming 0.35 @ dno.

Using the 95mm gives me a VD of 9.5v which is less than the 5% (11.5v) i need to be under.

Any thoughts on this method?

@davesparks i like the idea of parallel cables but would you do this using 2 swa or 4c in one swa?
 

Reply to Submain swa size check in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys Any advice/ pointers would be appreciated 😉 Have ‘pretty big’ new build house we’re wiring from scratch. New supply in from DNO is PME...
Replies
62
Views
5K
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Replies
7
Views
2K
  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
144
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
2K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top