Search the forum,

Discuss Sunbed shop. Breaker keeps tripping! HELP?! in the UK Electrical Forum area at ElectriciansForums.net

chreewebb

-
DIY
Reaction score
2
Hi there, I run a small sunbed shop with 2 sunbeds. (please bare with me as I'm not very electrically minded)

I have a problem with my sunbed tripping out. I have 2 sunbeds running off one board (Single phase). The board product number is QFS-MB7 and the main switch is rated as 100A. I used to have two breakers (RCBO 50/30/SP 50A 30mA) and these were fine, however during the summer as I got super busy they would occasionally overheat and trip out. So I then set up a blow fan and got an electrician to seperate the breakers in the hope it would dissipate some of the heat and fix the problem. All was fine until one of my employees forgot to turn on the fan to keep everything cool and the breaker ended up tripping so much it must have worn it down and then would trip even when the fan was on. So I then replaced both of the breakers with (what I thought were) better ones, the same breaker but a C TYPE which I was told was better when dealing with sunbeds/fluorescent tubes (50A 30mA (C Type) RCBO single module). These were the same brand as the old one however believe they are a cheap-ish brand as I only paid around £35 for the two new TYPE C breakers. All was going fine, and as coming into Autumn I have been quieter business wise. But now the new breaker is tripping out again and I'm not even as busy as I used to be! The breaker is warm to the touch but no where near as hot as what they used to be like when I had the old breakers in but it is still tripping and getting worse! Any suggestions on what you guys think it could be? I'm really stuck here and it is affecting my business as it is tripping out on a customer mid sunbed! Could it be the cheap breakers or? Thanks for any help!! I really appreciate it.
 
Also.. just found this info out from when I opened up (been open just under a year.) I was advised this from my sunbed supplier.

50amp type c breaker 100milliamps
10mil cable
50amp rated rotary isolated switch just above skirting boards left within 1 metre of sunbeds


Sunbeds run at about 45 amps


 
I wouldn't have thought it would be a problem with your distribution board, or your protective devices (MCB/RCBO) I think they will be doing their job and it will be a problem with the sun beds or associated wiring.
 
Hi there, I run a small sunbed shop with 2 sunbeds. (please bare with me as I'm not very electrically minded)

I have a problem with my sunbed tripping out. I have 2 sunbeds running off one board (Single phase). The board product number is QFS-MB7 and the main switch is rated as 100A. I used to have two breakers (RCBO 50/30/SP 50A 30mA) and these were fine, however during the summer as I got super busy they would occasionally overheat and trip out. So I then set up a blow fan and got an electrician to seperate the breakers in the hope it would dissipate some of the heat and fix the problem. All was fine until one of my employees forgot to turn on the fan to keep everything cool and the breaker ended up tripping so much it must have worn it down and then would trip even when the fan was on. So I then replaced both of the breakers with (what I thought were) better ones, the same breaker but a C TYPE which I was told was better when dealing with sunbeds/fluorescent tubes (50A 30mA (C Type) RCBO single module). These were the same brand as the old one however believe they are a cheap-ish brand as I only paid around £35 for the two new TYPE C breakers. All was going fine, and as coming into Autumn I have been quieter business wise. But now the new breaker is tripping out again and I'm not even as busy as I used to be! The breaker is warm to the touch but no where near as hot as what they used to be like when I had the old breakers in but it is still tripping and getting worse! Any suggestions on what you guys think it could be? I'm really stuck here and it is affecting my business as it is tripping out on a customer mid sunbed! Could it be the cheap breakers or? Thanks for any help!! I really appreciate it.

Hi-lighting the part here where you said you got an Electrician in... hmmm, tbh I'm not sure who you got in but it wasn't a competent electrician, he would have found the cause, rectified the issue and left you an happy customer IMHO.

You need to get a 'Competent Electrician' in this time, someone who will identify and rectify the problem.

Can you confirm the manufacturers expressed 100mA rated protection as you have 30mA at the moment and this could be due to regulations regarding install methods, without a site visit it all guess work here.

Due to the current flow is close to rating of device and high you would need a spacing between devices to allow dissipation of heat - this was a poor install by the sound of it from the original design point of view.
 
Last edited:
Holy crap, just been doing some research online!! and the notes I received from my sunbed suppliers were as follows..
50amp type c breaker 100milliamps
10mil cable
50amp rated rotary isolated switch just above skirting boards left within 1 metre of sunbeds
Sunbeds run at about 45 amps

I passed this info onto my electrician and have now realised he's put 30mA breakers in!! Wow! Guess that's my problem!
 
Holy crap, just been doing some research online!! and the notes I received from my sunbed suppliers were as follows..
50amp type c breaker 100milliamps
10mil cable
50amp rated rotary isolated switch just above skirting boards left within 1 metre of sunbeds
Sunbeds run at about 45 amps

I passed this info onto my electrician and have now realised he's put 30mA breakers in!! Wow! Guess that's my problem!


It may be but needs confirming, also it may not be as simple as refitting with 100mA protection, it depends on how the circuit has been installed, alterations or new circuit maybe needed to allow compliance with regulations.

Strange that the sunbeds have been design with such high leakage for sale in our market as other regulations may mean the install is subject tighter regulations.

Do you have a link to the model and manufacturer of the sunbed?
 
Last edited:
Holy crap, just been doing some research online!! and the notes I received from my sunbed suppliers were as follows..
50amp type c breaker 100milliamps
10mil cable
50amp rated rotary isolated switch just above skirting boards left within 1 metre of sunbeds
Sunbeds run at about 45 amps

I passed this info onto my electrician and have now realised he's put 30mA breakers in!! Wow! Guess that's my problem!

I cant see any point in a 100ma RCD unless disconnection times are not met by the MCB. Assuming that the MCB meets ADS requirements an RCD would be there for additional protection,and a 100ma RCD does not provide additional protection as required by bs 7671.
 
Last edited by a moderator:
Thanks for the replies! Just pulled this info off of a sunbed supplier website.

Lie down sunbed: Single phase: 45 or 50 Amp MCBThree phase: 3 x 20 Amp MCB
Vertical Tanning Unit: Single phase: 63 Amp MCBThree phase: 3 x 32 Amp MCB
Residual Current Device (RCD/RCB/RCBO) is optional, but if fitted must be 100mA trip, not 30mA.
Cable Single phase: 10mm Twin and Earth (Lie down and vertical sunbeds)
Cable 3 Phase: 3 x 4mm (Lie down sunbeds)3 x 6mm (Vertical sunbeds)

I'm running single phase and have stand up sunbeds. What would be my best route.. 2 x 63Amp MCB?

Thanks for the help guys, appreciate it.
 
Thanks for the replies! Just pulled this info off of a sunbed supplier website.

Lie down sunbed: Single phase: 45 or 50 Amp MCBThree phase: 3 x 20 Amp MCB
Vertical Tanning Unit: Single phase: 63 Amp MCBThree phase: 3 x 32 Amp MCB
Residual Current Device (RCD/RCB/RCBO) is optional, but if fitted must be 100mA trip, not 30mA.
Cable Single phase: 10mm Twin and Earth (Lie down and vertical sunbeds)
Cable 3 Phase: 3 x 4mm (Lie down sunbeds)3 x 6mm (Vertical sunbeds)

I'm running single phase and have stand up sunbeds. What would be my best route.. 2 x 63Amp MCB?

Thanks for the help guys, appreciate it.

It seems to have answered you problem in that you have the wrong breakers in if that is relevent to your model, I would get an Electrician in to confirm you can remove the 30mA protection although I don't really think your issue lies here and more in the fact you are running a larger load than you thought in the first place.. again test equipment to confirm so call a competent Electrician to do this and possible circuit alterations.

This can be a fire or shock hazard if not done correctly so please do not cut corners.

As you have been open 1yr I assume you had these supplies put in by a competent person, he may be liable for the alterations regardless if it is over a year..
 
Last edited:
Thanks for the replies! Just pulled this info off of a sunbed supplier website.

Lie down sunbed: Single phase: 45 or 50 Amp MCBThree phase: 3 x 20 Amp MCB
Vertical Tanning Unit: Single phase: 63 Amp MCBThree phase: 3 x 32 Amp MCB
Residual Current Device (RCD/RCB/RCBO) is optional, but if fitted must be 100mA trip, not 30mA.
Cable Single phase: 10mm Twin and Earth (Lie down and vertical sunbeds)
Cable 3 Phase: 3 x 4mm (Lie down sunbeds)3 x 6mm (Vertical sunbeds)

I'm running single phase and have stand up sunbeds. What would be my best route.. 2 x 63Amp MCB?

Thanks for the help guys, appreciate it.

As the spec is for 63a MCB's it would appear your present set up is overloaded. However you CANNOT simply change your 50a MCB's to 63a,it is essential that tests are carried out to verify disconnection times,and cables as installed meet the requirements of an uprated device.
 
I understand, thanks for the help.

Would I be able to run x2 63Amp MCB's off my board as it says Max Load: 100amp. The beds run at about 45amp each?

Will get an electrician to come do all the checks..
 
I understand, thanks for the help.

Would I be able to run x2 63Amp MCB's off my board as it says Max Load: 100amp. The beds run at about 45amp each?

Will get an electrician to come do all the checks..

We cannot possibly tell you as we do not have the load info for the vertical beds only the rating of the MCB's required.
 
Last edited:
Could anyone explain which kA rating I would need, 6kA or 10kA? Thanks, also what type would best suit me?
there again, tests would confirm the prospective fault current which would determine the kA rating of the breakers.
 
Could anyone explain which kA rating I would need, 6kA or 10kA? Thanks, also what type would best suit me?

It is starting to look like you are trying to do this yourself with a step by step guide, we have aleady explained you will need an Electrician and testing will need to be carried out as well as an evaluation of the existing.

I believe the advice we can offer now is at an end and you now need to discuss the rest with the Electrician you have been in contact with.

Closing thread.
 

Reply to Sunbed shop. Breaker keeps tripping! HELP?! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having trouble figuring this one out. House was built 5 years ago. Eaton box and breakers. Over the past 3 weeks, the bedroom breaker keeps...
Replies
8
Views
700
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
344
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
879
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top