Hi,

a recent PIR has picked up no RCD protection and no supplemantry bonding to pipe work.

Am i correct in saying if all circuits to bathroom are protected by RCD then supplementary bonding is not required?
 
Hi,

a recent PIR has picked up no RCD protection and no supplemantry bonding to pipe work.

Am i correct in saying if all circuits to bathroom are protected by RCD then supplementary bonding is not required?

Not quite true, it depends what type of installation you are talking about, SB is still required in a lot of cases.

If you are talking about domestic bathrooms, then all of these conditions need to be met to omit SB,

1) the final circuits meet the requirements for ADS
2) all final circuits in the location have additional protection by means of an RCD 30mA
3) all extraneous conductive parts of the location are effectively connected to the protective equipotential bonding (main protective bonds) to the MET
 

Reply to supplementary bonding and rcd protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
392
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
655
Just a thought guys in terms of RCBO’s and supplementary bonding. Obviously supplementary bonding isn’t required as long as a 17th / 18th...
Replies
5
Views
2K
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock