hi,

Popped round in laws house last night as they were having power loss issues. As I pulled up noticed the utility guys on their road hard at work sorting it out. So out of curiosity I thought I'd check the voltage readings as they had power but you could tell the voltage was low.

I was getting about 90v between live and neutral,
90v between neutral and earth
and no reading between live and earth

the property is down a country lane but new pme supply installed within the last couple of years. New Cable installed down the length of the lane.

1st they were looking at the transformer located on a pole then moved there attention to what i presume must have been a joint further down the road.

my feeble brain is trying to figure out what would cause those readings? is it broken earth or neutral?

cheers
 
I think I would have asked the utility guy's on the ground rather than asking on here for a answer. It's possible you would not get the right answer with remote guesses as to the problem
 
The fact you measured 90volts N-E on a PME supply is a lot more worrying to me than the issue that caused the missing phase.
 
didn't get a chance to ask them in the end as I had to shoot off. But problem seemed to be resolved later that night after they isolated for a a few hours.
Wasn't looking for definitive answers just curious to what would cause those readings.
 
hi,

Popped round in laws house last night as they were having power loss issues. As I pulled up noticed the utility guys on their road hard at work sorting it out. So out of curiosity I thought I'd check the voltage readings as they had power but you could tell the voltage was low.

didn't get a chance to ask them in the end as I had to shoot off.

So you went to the in-laws to sort out their power issues and achieved nothing as you didn't have the time to stop and ask the guy's in the know

But problem seemed to be resolved later that night after they isolated for a a few hours.

No doubt the utility men working down the road had to isolate to carry out the repairs

Wasn't looking for definitive answers just curious to what would cause those readings.

The fault down the road!!!!
 
didn't get a chance to ask them in the end as I had to shoot off. But problem seemed to be resolved later that night after they isolated for a a few hours.
Wasn't looking for definitive answers just curious to what would cause those readings.

Love it. Enough time to take voltage readings but not enough time to ask the guy down the road. If you don't like the In-Laws.... fair enough. Just pop round to gloat.. "Yeah, you got no power... haha, see ya later". Im not that keen on my in laws either, respect, I like the thinking.
 
Love it. Enough time to take voltage readings but not enough time to ask the guy down the road. If you don't like the In-Laws.... fair enough. Just pop round to gloat.. "Yeah, you got no power... haha, see ya later". Im not that keen on my in laws either, respect, I like the thinking.


Yeah, I've gotta show some sort of compassion....but not too much
 
So you walked away from a perfect learning opportunity, well done!

You could have found out precisely what caused the symptoms you observed, but no you came on here for a group of random guys to make wild guesses.
 
hi,

Popped round in laws house last night as they were having power loss issues. As I pulled up noticed the utility guys on their road hard at work sorting it out. So out of curiosity I thought I'd check the voltage readings as they had power but you could tell the voltage was low.

I was getting about 90v between live and neutral,
90v between neutral and earth
and no reading between live and earth

the property is down a country lane but new pme supply installed within the last couple of years. New Cable installed down the length of the lane.

1st they were looking at the transformer located on a pole then moved there attention to what i presume must have been a joint further down the road.

my feeble brain is trying to figure out what would cause those readings? is it broken earth or neutral?

cheers

didn't get a chance to ask them in the end as I had to shoot off. But problem seemed to be resolved later that night after they isolated for a a few hours.
Wasn't looking for definitive answers just curious to what would cause those readings.

So you walked away from a perfect learning opportunity, well done!

You could have found out precisely what caused the symptoms you observed, but no you came on here for a group of random guys to make wild guesses.


The worse bit is you could have passed on the information had you taken the time to find out what the fault was. First hand experience in a situation like that is hard to come by. By passing on knowledge others benefit.

61 posts to your credit, 17 of them asking questions………

Your one chance to give something back and you were too busy! Thanks!
 
You could have brewed up with that, take about 2 and a half times longer like.

6 1/2 times longer surely, unless you've got a constant-current kettle. Actually, where is my coffee? I'm sure our mains is at normal volts but it's taking a long time to appear...

Agree with Marvo - if the supply is PME, it takes some doing to get an N-E voltage like that at the consumer's terminals - with a normal TN-C-S connection it's more or less impossible. OP, How sure are you that there's not a polarity reversal somewhere there?
 

Reply to suppliers fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
516
Hi everyone, I'm new to the industry(Qualified a few months ago). I have a client with 6 LED light fixtures on the same circuit/breaker, 3 are...
Replies
3
Views
2K
I need an EICR done on a house I rent out in Reading, England - 4-bed detached built in early 1980s. Would ideally like someone from this forum...
Replies
2
Views
510
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock