Discuss Supply to a 63A RCB in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
14
Hi

I need to put a 63A RCB 6 way weatherproof consumer unit ( Garage unit ) with 2x6A , 2x20A , 1x32A MCB's, in my workshop at my farm , now the supply to it, comes from the Main 83A 3 phase fuse box on the other side of the wall where I want to mount this unit , the length of cable would be around 500mm max .

Question , with it being such a short length of cable for the feed could I use a 6mm2 cable ! , as I have loads of it, but no 10mm2 .


cheers


spike
 
There is no ocpd on the supply , apart from the main 3 phase 83A 30mA RCD trip switch coming into the Farm , basicly I am wanting to know if a short length 400mm of 6mm2 cable will take the load of a 63 amp 30mA double pole RCD trip switch .
 
83A rcd is your protection??? So as this isnt an ocpd you must be relying on DNO for ocpd on this submain? i think you need rethink your design, whats the earthing arrangement.?
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.
 
Hi

Thanks for your feedback , the lights (lights 60W ) are only for the Tack room x1 and grain store x1 , chicken room x2 , the sockets are for these rooms only , they are part of the main workshop ( but they are separated ) it all was the Cow shed !.

The Main workshop wiring is fine ( off the blue phase ) , anyway what I have done is :

Have changed the Main supply fuse feeding the 63A RCD from 83A to a Lawson 63A ,( this is off the Yellow phase , house is off the Red phase ) and used a 10mm2 cable to supply the 63A RCD , yes I know I really should put in 16mm2 tails ! , needed it doing today

ps: I would not do anything until I was 100% sure it was right , that is why I am asking the questions , maybe stupid questions but if I get the correct answer at the end that is what I will do ! , not before .
I am not a Electrician as you have guessed , I am a time served mechanic so I do have a bit of savvy about me , not a lot but a bit ! , as they say in my trade you learn something everyday ! .

spike

Read more: Supply to a 63A RCB - http://www.diynot.com/diy/threads/supply-to-a-63a-rcb.467722/#ixzz4Ltk1uUJ4
 
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.
 
It would have been cheaper, safer and legal to have bought the right size cable.
Choosing to work illegally and unsafely for greater cost it not generally the best approach.
However you are unlikely to overload any parts with the set up as you have described.
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 

Reply to Supply to a 63A RCB in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
630
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
448
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
534

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock