Hi all

question regarding the length of surge protector cables. I have read the reg 534.4.8 that states that the length should not exceed 500mm. Is that for each conductor so every conductor should be 500mm or less. So with a 3 phase surge protector all 3 phases/neutral and earth should not exceed 500mm is that correct ? Thanks in advance ?
 
No, I mean that is the answer, the line conductor and PE should ideally not exceed 500 mm and in no cases exceed a meter.
Same applies to the neutral and PE.
 
This could be pretty much impossible to be able to install a SPD on a three phase board external as some consumer units have there earth bars at the top of the boards so defo exceeding 500mm. Could be well over a meter ?
 
This could be pretty much impossible to be able to install a SPD on a three phase board external as some consumer units have there earth bars at the top of the boards so defo exceeding 500mm. Could be well over a meter ?
The Length can be reduced by simply bolting the PE to the earthed chassis of say the DB enclosure, rather than using a separate conductor and adding to the length.
See Hager’s version
 

Attachments

  • 7825CCF8-A633-457D-BD4F-469E88A3E4C7.jpeg
    788.1 KB · Views: 21
Oh right yeah, they look decent no cable connections either. So to clarify on a three phase consumer unit. It’s the length of the any phase conductor and earth conductor combined that can’t be over 500mm ?
 
Oh right yeah, they look decent no cable connections either. So to clarify on a three phase consumer unit. It’s the length of the any phase conductor and earth conductor combined that can’t be over 500mm ?
Yes pretty much, it can exceed 0.5 meters but not 1meter.
 

Reply to Surge protection cable length in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I have above mentioned breaker which does not have any markings to show which is the neutral pathway, I wish to fit it directly above a 3 phase 4...
Replies
2
Views
794
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
752
Hi there just a few questions I have to do an install of a small ware house that was built in 2021 January (finished) client that is going into...
Replies
2
Views
953
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
854

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock