Hi guys,

I am running a supply to an outbuilding that requires a 22m run from the Main CU (in the garage) to the CU in the outbuilding, at the Main CU it will be a 40A MCB supplying an 63ma RCD protected sub board which will then supply:

6A type B MCB for 12 downlights and an extractor fan
32A type B MCB for 3 double sockets
20A type B MCB for a 3.5kw split air condition unit

I've calculated the voltage drop if using 6mm 3 core SWA clipped direct (table 4E4A p372 BS 7671) 53 x 40A x 22m / 1000 = 46.64 Vdrop .. thats a crazy figure

And the supply will be feeding a sub board initially based on what I've been taught I calculated maximum demand by adding the breakers amp size and x them by 40% so 6+32+20 x 40% = 23.2A

The SWA will run up the outside wall from the garage into the loft and out the other end, and down galvanised conduit, into the ground and into and up a wall with insulation (2m) and into the outbuilding

The queries I have are:

The majority of the run will be clipped direct and only a small part of the length will be in insulated brick wall am I right/wrong to assume Reference method C (clipped direct)?

And as it is SINGLE PHASE 3 CORE cable I'm using I'm a little confused as the only two options under clipped direct in table 4E4A (p372 BS 7671)is '3 CORE 3 phase AC' and '1 two core cable SINGLE PHASE AC' my installation does not fall perfectly into either option, which should I select?

And how best would you recommend lowering the Voltage drop to the stipulated 5% 11.5V?


Thank you in advance for helping,

Mark
 
If the description of single phase or three phase phase wasnt obvious enough then consider that you will only be using two of those three cores that you have, therefore treat it as a two core cable. The ccc tables are only concerned with the cores which are carrying current under normal conditions for, what are hopefully, obvious reasons.

Do not use the values from table 4e4a for the voltage drop calculation, that table details the current carrying capacity of the cable. Use the values from table 4e4b on the following page which is clearly identified as being the table of values of voltage drop per ampere per metre.
 
Is this calculated in a different way? apologies for the nativity of the question.

The calculations are the same, its your metnod which is wrong.

Your apologies are irrelevant, you should have finished making this kind of mistake before you started dsigning circuits for the real world without supervision.

Trusting to a bunch of strangers on the internet will almost certainly invalidate your insurance and not be a valid defence in court should it all go wrong.
 
Taking pity...a few hints.
This is a distribution circuit. Therefore if you calculate allowing for the maximum volt drop on the distribution circuit only that will not allow for volt drop on any final circuits connected to the distribution circuit.
You also need to take into account that where a lighting load is to be supplied the maximum permitted volt drop requirement is not 5%.
Refer to App 12.
 
Last edited by a moderator:
I've calculated the voltage drop if using 6mm 3 core SWA clipped direct (table 4E4A p372 BS 7671) 53 x 40A x 22m / 1000 = 46.64 Vdrop .. thats a crazy figure

where did 53 come from.? the mV/A/m for 6mm is 7. so:

( 7 x 40 x 22 ) /1000 = 6.16.
 
I've calculated the voltage drop if using 6mm 3 core SWA clipped direct (table 4E4A p372 BS 7671) 53 x 40A x 22m / 1000 = 46.64 Vdrop .. thats a crazy figure

where did 53 come from.? the mV/A/m for 6mm is 7. so:

( 7 x 40 x 22 ) /1000 = 6.16.

He's used the CCC for 3 or 4 core 6.0mm from table 4E4A....53a!
That would rather skew the result.
 
i sympathise with your kitchen table. i got 2 wonky legs (even when sober).
 
Hi guys, thank for you for all the helpful posts! it was late lastnight when i was posting so i was looking at the wrong page for the Vdrop and actually looking at the current carrying capacity as Davesparks pointed out.

But this has now raised up another related issue about voltage drop with the sub board distribution cable, I've calculated that i need to up it to 10mm SWA for such a run of 22m but also there's the combined Vdrop from the circuits on the sub-board that i need to account for EG. the Vdrop for the length of the circuit from the Main CU to the Sub-board + the Vdrop from the Sub-board MCB to the end of the lighting circuit on that board.. How do you combine two different voltage drops? (ie the lighting circuit must be within 3% and the distribution circuit must be within 5%, or do you treat thee two circuits independently?
likewise for the ring circuit on the sub-board they would both be 5% do they have to both add up to be less than 5% or is there another figure to go from?

any insight would be greatly appreciated.

Something I do regularly where an SWA drops down a wall into the ground. A meter or so of galv with a bushed top protects the cable from damage from strimmers and such like.
I'v chosen to run a part of the SWA in galv conduit as it will run past an outdoor step and be about 2 inches from the ground just for added mechanical protection from people kicking it or from some garden tools hitting it (just trying to account for worst possible situation)

Is this the same house as your other thread.
my other thread on here about alternate cables for external use is for the same house but is not related to the sub-board/sub-distribution cable.
 
Hi guys I've attached a photo, at the roof of the bungalow (i've marked this in red) is where the SWA will come out of and down the wall, where it is marked in blue is the area I am concerned maybe 'at risk' from kicks and other problems from people walking past. The client has stated that the bit in blue that runs horizontally in front of the step will be concreted over once his outhouse has been completed.

sub board supply.jpg
 
Hi guys I've attached a photo, at the roof of the bungalow (i've marked this in red) is where the SWA will come out of and down the wall, where it is marked in blue is the area I am concerned maybe 'at risk' from kicks and other problems from people walking past. The client has stated that the bit in blue that runs horizontally in front of the step will be concreted over once his outhouse has been completed.

View attachment 37579
What size galv conduit are you intending to use? 10mm2 2 core it will be a tight job to run that in conduit.
 
Pete999 - I'm going to spec the job again later today as things have changed somewhat from initially using 6mm to now using 10mm SWA, after reading everyone's advice I may leave out the galv conduit and run the cable clipped direct.
 
calculate VD for the sub first. from my previous post, for 6mm this would be 6V assuming a 40A load ( which is a bit pessimistic. then, calc. the shed VD.. add them together.
 
Pete999 - I'm going to spec the job again later today as things have changed somewhat from initially using 6mm to now using 10mm SWA, after reading everyone's advice I may leave out the galv conduit and run the cable clipped direct.
or just use some plastic duct. and i think 10mm is overkill.
 
calculate VD for the sub first. from my previous post, for 6mm this would be 6V assuming a 40A load ( which is a bit pessimistic. then, calc. the shed VD.. add them together.

I've calculated the Vdrop for the 10mm SWA on 40A MCB from the main board at 22m length run which comes to 3.8VD (1.68% of the allowable 5%)

The issue is the circuits coming off the sub-board.. for instance I've calculated the 2 double sockets that the client wants needs a run of 2.5 twin and earth on 32A MCB and 12m length run which comes to 5.76VD (2.5% of the allowable 5%)

IF i add these two figures together 1.68% and 2.5% i get 4.18% which is just below the allowable 5% (11.5V)

Am i right to add it like this and then do the same for the other circuits (lighting VD + 10mm SWA VD and air con VD + 10mm SWA) on the sub-board or should I treat them all individually and not add the figure for the VDrop figure for the 10mm SWA
 
personally, i add the voltages first, then work oyt the %. i'd not be too worried if the figure was over the 3% anyway. you got 10V to play with due to the silly 230V nominal voltage rubbish figure.
 
The total volt drop from the origin of the installation must not exceed 3% for lighting. For example if your distribution circuit is expected to carry a maximum load of 40a then the volt drop of both distribution circuit and the furthest point of the lighting circuit combined must not exceed 3%. Therefore you will calculate the maximum volt drop on your lighting circuit and add it to the calculated voltage drop on the sub. In total it should not exceed 6.9v
Put another way if your lighting circuit will have a VD of 2v from the CU then your distribution circuit fully loaded will have a permitted volt drop of 4.9v.
 
Last edited by a moderator:
and if the supply voltage drops within permissible limits, e.g. @peak times, that's a drop of 6% which makes a mockery of your 3%.
 
Nobody has mentioned the reference method. Clipped direct has a higher ambient temperature than buried, which is usually lower as it's cooler below 500cm. So, go for the one which has the higher impact on the temperature of the cable, so at least choosing clipped direct was right. And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend
 
Nobody has mentioned the reference method. Clipped direct has a higher ambient temperature than buried, which is usually lower as it's cooler below 500cm. So, go for the one which has the higher impact on the temperature of the cable, so at least choosing clipped direct was right. And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend
Think the OP has already binned that idea
 
Hi all, Thank you for your feedback you were right I have scrapped the SWA in galv conduit idea.
Just a quick one would I be able to use 6mm SWA as the subboard distribution supply as I have spoken to another spark I know who thinks this would be adequate hence why originally thought that would do, and also I remeasured the run and its 30m of SWA not 22m as stated before.

Regards,

Mark
 
40A through 6.0mm SWA is well within it's capacity. that's why i said 10.0mm was overkill.
 
At 30m the volt drop would exceed the permitted maximum though..(going by the book)....though in practice we all know 6.0mm would be perfectly OK.
yeah, but OP has used 40A for his Ib. in practice 25 - 30A would be more realistic.
 
And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend

The point is protect the cable from damage, any damage to the sheath allows water ingress which will rot the armour and make the cable unsafe.
The steel armour is there to connect a metal object penetrating the cable to earth, if the sheath is damaged and the armour rusts then it will no longer perform this function properly.

Luck is not required, just the correct sized conduit.
 
And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend

The point is protect the cable from damage, any damage to the sheath allows water ingress which will rot the armour and make the cable unsafe.
The steel armour is there to connect a metal object penetrating the cable to earth, if the sheath is damaged and the armour rusts then it will no longer perform this function properly.

Luck is not required, just the correct sized conduit.
 
I've just calculated this and it IS 10mm, it can't be longer than your previous measurement and be a smaller conductor!!. If your friend says it's overkill, I hope can be at the enquiry with you to explain the fire

What fire are you predicting here? 6mm SWA has a ccc of 49A single phase clipped direct at an ambient temperature of 30c which is well above the nominal current of the circuit.
 
What you need to do is calculate your volt drops for the distribution circuit and the final circuits based on your design currents for those circuits.
The VD on the distribution circuit will add to the VD on each final circuit giving you three values, one will be for lighting and must not exceed 3% (6.9V) the others are non lighting and must not exceed 5% (11.5V).
Select your distribution cable based on one that complies in all cases.
Check that you are not likely to exceed CCC (very unlikely) or Zs limits.
E.g. If you had 230W (1A) of lighting/extraction on a 10m final circuit, two sockets each possibly taking 10A (very variable, normally you take the In for sockets) one at 7m and one at 12m and 15A for the AC on a 10m circuit then the calcualtion coudlba as the attached diagram.
Volt drop for 3 circuits.jpg
Note you have no short circuit discrimination between the supplying MCB and the final circuits, if you are installing 2 double sockets why is it a ring, a 20A radial may be easier.
 

Reply to SWA armour supply to outbuilding, what CSA cable? and Reference Method? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
865
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
987
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
527
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock