Keef

Topic of much debate...
Is there reasons to fit the earth tag on the inside of the metal enclosure? The one about preventing corrosion does not wash with me as the enclosure is not IP68 rated thus cannot protect from corrosion inside.
I have always been taught to fit brass tag on the outside with a brass nut and bolt to prevent electrolytic corrosion. If you fit brass tag on the inside you get brass(tag)-mild steel(enclosure)-brass(tag)-zinc plated nut. Not a good mix especialy when adorned with another mild steel roofer!
Any oppinions welcome, this could be a big can of worms though. DISCUSS...
 
I would always have fitted the tag on the outside because that gives the best contact between the brass gland and the tag. Wether the tag is bolted with a brass or galv bolt shouldn't really make any difference to the connection as the bolt only holds the tag as tight as possible to the box unless you are fitting a secondary tag to the bolt for an earth connection within the box and in this instance a brass bolt is preferable . It's hard to see where the bolt type would make any difference to galvanic/electrolic action as the bolt is going to be making the same contact to a galv box either way, as is the tag. In an area of salt air the galvanic/electrolytic action will be increased and in these areas a non metalic box is preferable with all tags/earth connections within the box.
Once all connections are tight on a galv box I have found it advantagous to paint the outside of the box with hammerite and put a bead of silicone around the lid and holding screws and also around the exposed armour to seal the gap within the gland, but that is because a lot of my work has been around the local harbour. Also always fit the supplied boot.
 

Reply to SWA Gland (correct termination of) in the Australia area at ElectriciansForums.net

Similar Threads

Hi all. I have noticed there are two schools of thought here when running a separate earth with a SWA to a large DB, where is the correct place to...
Replies
2
Views
1K
I've an otherwise small and simple job to do later, out of hours, fit an outdoor IP FSU for a small AC unit fed from an outdoor socket on an RFC...
Replies
12
Views
2K
Hi I have been in the electrical contracting industry all my working life 40 years and became a member of the NICEIC in 2006. During this time I...
Replies
17
Views
2K
S
Hi, i would like to make sure i understand this properly. On a TNS supply, using 3 core SWA to run a sub-main, and using the third core for CPC...
Replies
6
Views
4K
K
Hi all, This is my first post, so here goes. I recently terminated SWA in an IP66 Wiska box with the CPC and Steel linked together at the...
Replies
8
Views
3K
Guest112
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock