Search the forum,

Discuss Switched Fuse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1,228
Hi,

Just a a quick one, I fitted this switched fuse today.

i dropped the cable off yesterday and the builder (nice bloke) dropped it in the trench, packed with sand, warning tape etc, 1m deep. Nice job. Then back filled to the top.

Anyway, I get there today and he had only left a poxy bit of cable poking out into the new cupboard.

i have essentially out the load side in the dead when off side of the switch inside as you can see, I only did this as I felt it would be better to do that than extend it and add another joint.

i have suitably labelled it since the photo saying its live etc where the fuses are and you need to isolate at the DP isolator adjacent.

would you leave it as is or swap the lives around do it's the correct way, but would just need to crimp a section in. I can't see any harm in leaving it as it is myself, just looking for other opinions.

just to add, I have put a fly lead from the banjo but not shown in this photo, and I am using a TP switched fuse because there is simply more space in it, I am not in to forcing stuff in to small enclosures, the customer was happy with the price and I'll enjoy the job more.

image.jpg
 
Last edited:
Just to add this is having a new supply from the road put in next to it. This is a new supply for a house, this cut out is 30m from the road, but 30m from the house too. Dont ask why it's here where it is.
 
Why a triple pole switch fuse for a single phase supply? Also doesn't seem to be any flylead from the banjo.
 
I did put a lead from the banjo to the other bolt where the earth is, just not shown on this photo.

i used this switched fuse as it's simply got more space in it, why struggle with a small enclosure when you don't have to.
 
I can't see the picture but if I've got the gist of the OP right then you need to have a switch fuse arranged such that the fuse is downstream of the switch. This is so that the switch isolates the fuse for it to be replaced safely. Also they are generally designed so that all of the internal links etc are after the switch so that turning the switch off makes it relatively safe to remove the cover and work on it.
I have in the past fitted one or two KMF switch fuses upside down purely to make it possible to connect the right way round.
 
I've got to go back tomorrow anyway so I think I'll probably just extend it to swap it round, unfortunately there was just not enough length in the cable to do it the right way round to start with.

i was just avoiding another joint you see.
 
Ok I can see the picture now.
If you'd fitted a smaller switch fuse or fitted it lower down it would have reached.

Also the banjo appears to be inside the box and not in good contact with the gland body?
 
I couldnt physically get it any lower as the cable wouldn't bend, that's 25mm 3 core.

the banjo is making a good enough connection, it's sodding tight, it's not like it's being used as the earth, it will be connected the other end too.
 
I have to agree with Davesparks, I don't see why you couldn't have glanded the cable lower and mounted the switch fuse in a better position to give you enough to get into the top!
 
I couldnt physically get it any lower as the cable wouldn't bend, that's 25mm 3 core.

the banjo is making a good enough connection, it's sodding tight, it's not like it's being used as the earth, it will be connected the other end too.

So use a spreader box or a bit of galv trunking to get over it.
There's always a way with a bit of creative thinking and care, at the moment it looks a bit rough.
 
I reckon your going to be stuck with a compromise on either correct function,or tidy cabling...not both.

All this stems from not being there,when the cable you specified and selected,was installed.

Not jibing your job,seen plenty where the installer would be ashamed of photos,but even marking a big,horizontal line,in yellow line marker,for the "trench dude" to pull cable to,does not guarantee correct fitting.

You really have to be there.

...And if you were,all this would be academic!

...I'm at least confident you will have plenty spare,at the other end :38:
 
at the moment it looks a bit rough.
I would have to disagree, it looks far from rough, what is rough about it eh?

I reckon your going to be stuck with a compromise on either correct function,or tidy cabling...not both.
I told him to leave 1m - 1.5m poking out the end of the pipe which he didn't, he then back filled a 30m trench... not exactly the possible to move.

A couple of terminal blocks to extend the cable and you are good to go!
It's ok, ill just swap the lives around and crimp and heat shrink, it will look fine.

You must be really struggling to find something to pick holes in on this one.....splitting hairs or what?
Thanks.
 
You can see here the pipe and the cable coming out of it. It was not particularly possible to bend it any further, it is not exactly flexible stuff.

I got it as low as it would go, its very easy for you all to say move it lower, but as none of you were there doing it....

2016-05-19 12.29.03-1.jpg
 
If you fit a single phase Switched fuse that takes up less space in the box, could you then not fit it lower down in a more central position? Might leave enough space above to get the other gubbins in you need?
 
I was keeping it over to one side as WPD have got to put a cutout in there and also the meter and I didn't want it all crammed in, it made more sense keeping it to one side.

You could say fit a single phase switched fuse, but the SP equivalent is significantly smaller and just a pain in the --- to work with, I would rather not struggle with it.

Like I say, the central position would have been more in the way.
 
Forgive me for what is probably such a basic question, (and especially since I'm probably wrong), but shouldn't the load side go to the top edge of that isolator with the supply entering the bottom?
 
Did you actually tell your builder buddy how much SWA to leave at the intake position? or did he, like most builders think " Ah that'll do it's only electrics" been in this position many times, usually leave a note in plain English exactly what you require.
 
isn't the post suggesting the armoured is too short to so he has had to put load and supply the opposite way around?

It's just one of those things, the OP couldn't be there to get the right amount of cable, the Builder did what most builders do when you ask them to do something, "well I did leave some cable for you" still think I would have fitted a SP switch fuse, but it's not my job so who am I to complain.
 
I think the crux of the post is that the armoured is too short. Isolator hasn't been mentioned as far as I can see.

Sorry, you were referring to the isolator not the switch, obviously as that's what you wrote. my bad.
Now I'm probably gonna get shot here but assuming the fused switch also switched the neutral, which it looks like it doesn't, would you need an isolator?
 
Sorry, you were referring to the isolator not the switch, obviously as that's what you wrote. my bad.
Now I'm probably gonna get shot here but assuming the fused switch also switched the neutral, which it looks like it doesn't, would you need an isolator?

There is a double pole isolator just to the right of the box that will suffice.

Personally I'd look at moving the box over to be directly above where the SWA comes from the ground. I bet there will be enough length then to terminate into the top side of the isolator.
 
Could you not have chopped the duct off flush with the floor to give a bit more wiggle room on the cable?

Wylex make a single phase switch fuse with plenty of room to terminate a 25mm
 
Get a new builder!
He has also brought the cable in centrally whereas you need to be either left or right, if the cable had not come in centrally you would have been able to bring the isolator down directly over the cable.
Happens all the time.
 
I think we have reached the part in "Life of Brian",where the Peoples Front of Judea,are discussing what action to take...

If the builder was told how much cable to leave exposed,and he has not,then maybe it has tape,maybe it is a meter deep,maybe it is not gnarled...and maybe not.

I do not believe it will look shabby in the end,just not as it could,and certainly not worse than more than half of similar jobs i have seen.

If you select,specify,quantify and are installing a cable...be there for the bit that cannot now be altered.

My boyhood physics teacher,issued as a punishment,the writing of an A4 sheet of descriptive prose,on the inside of a ping-pong ball...

This thread is getting there...
 
Absolutely, definitely, connect the supply to the switch and the load to the fuses. In theory it's nice to minimise joints but not at the expense of doing the job wrongly. Properly crimped and heatshrink-insulated joints are reliable and safe and I can't see your objection to using them here, to me it's a no-brainer.

E2A, what is the point of the separate isolator? Could you convert the TP SF to isolate the neutral by putting a link in one pole in place of the fuse?
 
Last edited:
Could you not have chopped the duct off flush with the floor to give a bit more wiggle room on the cable?

Wylex make a single phase switch fuse with plenty of room to terminate a 25mm

Yep agreed.

The Wylex 110M have plenty room for the SWA that has been used. Not to mention it is also a DP isolator too - two birds one stone etc!
 
Yep agreed.

The Wylex 110M have plenty room for the SWA that has been used. Not to mention it is also a DP isolator too - two birds one stone etc!

That would of been my 1st choice. I install these all the time on new build flats with 25mm 3 core SWA and 25mm tails. And if the duct was cut down lower uksparks could of got a better sweep on the cable and would of been easier to get the switch fuse lower.
 
looks fine mate, you have done your best and functionality wise it works the same. Cant have every job your own way, just put it down as a blimp in your otherwise tidy work. Plus that banjo is fine as it is, i see where your coming from in regards to the larger switch for more accessibility and ease of install, why make lift hard...
 

Reply to Switched Fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
804
Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this...
Replies
15
Views
1K
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock