Search the forum,

Discuss T & E in conduit calculation help please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

MikeWindsor

Hi Guys, I apologise in advance as I have done this a**se about face, I have just finished putting power to my shed ( I am currently training to become a sparks got my 17th edition at pass in Watford shortly) and hoping to use my shed as my part p inspection as hoping to join ELECSA. Anyhow I have run 6mm T and E in 20mm plastic conduit, the run is about 10metres long and it had to go up and around a gate on its path to the shed (its all solid driveway so couldn't bury anything) so there are 7 x 90 degree elbows (never again !) and I want to make sure I have the correct rating but not sure how to work it out ? The OSG page 135 gives me a Cable factor of 58 then on page 136 is a multitude of figures for Conduit Factors but I cant seem to find a formula ?
Much obliged for any enlightenment ! Many thanks Mike

PS Next time I shall learn to terminate SWA instead !
 
Where to start ? Well first of all you deserve a medal, for geting a 6mm T+E through a 20mm conduit and round 7 elbows. Then you deserve it taking off you straight away for choosing such a silly wiring method.

For cable calculations, everything you need to know reference wise is in appx 4 of the regs. Follow the calculations like you have been shown in your training and you won't go far wrong. Easy eh ?
 
Hi Guys, I apologise in advance as I have done this a**se about face, I have just finished putting power to my shed ( I am currently training to become a sparks got my 17th edition at pass in Watford shortly) and hoping to use my shed as my part p inspection as hoping to join ELECSA. Anyhow I have run 6mm T and E in 20mm plastic conduit, the run is about 10metres long and it had to go up and around a gate on its path to the shed (its all solid driveway so couldn't bury anything) so there are 7 x 90 degree elbows (never again !) and I want to make sure I have the correct rating but not sure how to work it out ? The OSG page 135 gives me a Cable factor of 58 then on page 136 is a multitude of figures for Conduit Factors but I cant seem to find a formula ?
Much obliged for any enlightenment ! Many thanks Mike

PS Next time I shall learn to terminate SWA instead !
:smilielol5: who says the trade is losing quality standards?
 
I would point out that the conduit factors in the OSG are for single core cables, because you do not run T&E in conduit (normally).
If you were trying to calculate for 6 / 6 / 2.5 you would use 58+58+30 = 146 then turn to the next table look at a ten meter run and then find that it does not cover more than two bends for a 10m run. This would probably be because, since the conduit has to be constructed fully before pulling in, you would never get the cable down there.
 
Ha ha thanks guys for the abuse ! (I do have a sense of humour, you have to when you are 44 married with two young kids and starting a new career ! That you have no clue about) I did wonder what I was doing when I was trying to thread the elbows, although I did find a technique that made it easier towards the end, I am worried about all the black scraping on the PVC though. I was advised to use conduit by a retired electrician, he showed me his garden which he has used conduit to run lighting etc he swears by it ! However when I told him I had used 6mm cable he laughed and said " are you wiring in a kiln so your wife can take up pottery ! " 1st elbow out the house, 2nd elbow up the gate post, 3rd elbow across the top of the gate opening on batton, 4th elbow down the gate post, 5th elbow along the gravel board of a fence 6th elbow through the gravel board straight run to shed, 7th elbow into shed ! Luckily it is my house and not a customers, I not let loose on those yet ! know I have a long way to go and only just started in this industry but I am keen to learn from you experts ! I know I should have used SWA so may be I should use something else when I do eventually try and join a scheme !
 
I would point out that the conduit factors in the OSG are for single core cables, because you do not run T&E in conduit (normally).
If you were trying to calculate for 6 / 6 / 2.5 you would use 58+58+30 = 146 then turn to the next table look at a ten meter run and then find that it does not cover more than two bends for a 10m run. This would probably be because, since the conduit has to be constructed fully before pulling in, you would never get the cable down there.

Thanks Richard for explaining, do you think I could split the run down from 10 metres into smaller lengths with the bends then total them up to get the conduit factor ?
 
I would point out that the conduit factors in the OSG are for single core cables, because you do not run T&E in conduit (normally).
If you were trying to calculate for 6 / 6 / 2.5 you would use 58+58+30 = 146 then turn to the next table look at a ten meter run and then find that it does not cover more than two bends for a 10m run. This would probably be because, since the conduit has to be constructed fully before pulling in, you would never get the cable down there.

Sorry another question why does the conduit have to be fully constructed first ? I pulled each piece as I added it ?
 
Thanks Richard for explaining, do you think I could split the run down from 10 metres into smaller lengths with the bends then total them up to get the conduit factor ?
Could do but your results would be odd as you could use smaller conduit for each section compared to the whole run.
e.g using 147 2m and 2 bends = 16mm conduit, 4m and 2 bends = 20mm conduit!
Sorry another question why does the conduit have to be fully constructed first ? I pulled each piece as I added it ?
To ensure that you can pull cables again at a later date if changes need to be made (and if buried in structure 522.8.2 applies) but may be a bit OTT if it is easy to disassemble.
 
Thanks Richard that all makes sense now, I think I am going to rip out the conduit and install swa I dont want the inspector to think I am a muppet ! Really want to do this right and be a professional ! I will just have to put it down to experience :6:
 
It's by far the ideal route, and you need to be under no illusion that there will huge gaps in your experience and knowledge after you have been relieved of your money,

Andy, I'm sure you meant to say ''It's by far ''NOT'' the ideal route''
 
When you call the scam provider I just tend to ask for Alex.....He like a good drink and is open for a dropsy of say £200 ish.....there ya go jobs a good un and your good to go. Remember though as far as I know only Alex is amiable like this.:stooge_curly:
 
There's already several existing threads about industry deskilling please rather use those to discuss the merits of limited scope quals and suitability for scheme registration.
 
Hi Guys, I apologise in advance as I have done this a**se about face, I have just finished putting power to my shed ( I am currently training to become a sparks got my 17th edition at pass in Watford shortly) and hoping to use my shed as my part p inspection as hoping to join ELECSA. Anyhow I have run 6mm T and E in 20mm plastic conduit, the run is about 10metres long and it had to go up and around a gate on its path to the shed (its all solid driveway so couldn't bury anything) so there are 7 x 90 degree elbows (never again !) and I want to make sure I have the correct rating but not sure how to work it out ? The OSG page 135 gives me a Cable factor of 58 then on page 136 is a multitude of figures for Conduit Factors but I cant seem to find a formula ?
Much obliged for any enlightenment ! Many thanks Mike

PS Next time I shall learn to terminate SWA instead !

Next time learn how to form 90 degree bends in the conduit without using elbows!! ;)
 
Sorry can't help really, only to say it's a bit of a rough old job, 6mm T&E in 20mm plastic tube with 7 90 degree bends really come on.
 
Words fail me. Yet again, and again, and again, we've a thread where the only best advice to the OP is to go and get trained properly. Half a clue is Zero an answer.

That being said, maybe a career in comedy instead? I think most of us would have been thoroughly entertained by the sight of 6mm TE in 20mm with 9 elbows!!
 
That being said, maybe a career in comedy instead? I think most of us would have been thoroughly entertained by the sight of 6mm TE in 20mm with 9 elbows!!


Even better get him to do it with real conduit not plastic. Let’s see him put the cable though the elbow and then screw it up.

It would be a screw up.
 
Yikes. I've been away for a short while and find mods are moderating and Eng54 isn't ripping the arse out of a post. What will the world come to I ask!?

The op says in the original post he doesn't know how to terminate SWA but wants assessing by a scam. Aren't they going to ask why the cable run wasn't done in SWA? And he's going to say 'we haven't covered that on the course'! Pay the money, hand out the chocky biscuits and let them rubber stamp the application, else fit some SWA and of you can't terminate correctly brodge the cable ends and throw in a couple of BS951 clamps. That's what they do around here :)
 
Well I typed out a response to this but then realised it wouldn't fit in with the touchy feely hug a Electrical Trainee approach that seems to be the way forward now.
So I'll just say that words fail me. That way I can't get told off.
 
mods are moderating and Eng54 isn't ripping the arse out of a post. What will the world come to I ask!?

The world has come to, I am sadly led to believe, a place where sadly E54 is currently finding himself being post by post moderated in order to maintain the party line and not upset half the forums sponsors by speaking the truth about Electrical Trainee's. Although, from posts like this one they clearly are not afraid of advertising their own incompetence to a global audience.

It would seem the state of the UK electrical industry is not the only organisation in denial.
 

Reply to T & E in conduit calculation help please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, My first post so hopefully I am correct in posting it here. My question is, I am thinking of an IP rated outdoor socket for the back garden...
Replies
3
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock