Discuss Temp hooking up a pair of 16a ovens for Christmas day.. in the UK Electrical Forum area at ElectriciansForums.net

Deuce

-
Esteemed
Reaction score
420
Hi all,

Our kitchen is going to be ripped out and replaced in the new year, and currently has just one small oven in it - I have 10 guests for Christmas dinner and it ain't going to be up to the job!

However, I already have two new built in single ovens delivered but uninstalled and a carcass from the new kitchen that I can put them in temporarily to make them usable.

My thinking is that there whilst not at all acceptable as a permanent solution, there should be no problem with me pulling the front of the existing FSU (40a cable and 32a MCB protection in place back to CU), and putting in a couple of cables on the load side with 16a commando sockets on them, and then 16a plugs on the ovens. I know the ovens will not exceed 16a and will be unlikely to even exceed 13a as I won't be using the grill element, I assume there is also a reasonable headway included in the 16a rating.

Or... Am I overthinking this and could make it even simpler by just plugging them into standard 13a sockets on two seperate RFC's using a 13a plug on each? If it doesn't blow the fuse... and I really doubt it would, is there an technical reason this would not be safe?

It goes without saying that whatever the temp solution, I'll be with the ovens the entire time they're used and would give them a test run ahead of the day.

Thoughts?
 
By far your easiest and cheapest solution will be to put them on 13A plugs. There's nothing in itself wrong with the 16A solution you suggest (except technically you'd need to have a reducing CPD involved as well down to 16A, so realistically that's a small garage style DB involved too) but it's a lot of work and expense for no real benefit.
 
Hi all,

Our kitchen is going to be ripped out and replaced in the new year, and currently has just one small oven in it - I have 10 guests for Christmas dinner and it ain't going to be up to the job!

However, I already have two new built in single ovens delivered but uninstalled and a carcass from the new kitchen that I can put them in temporarily to make them usable.

My thinking is that there whilst not at all acceptable as a permanent solution, there should be no problem with me pulling the front of the existing FSU (40a cable and 32a MCB protection in place back to CU), and putting in a couple of cables on the load side with 16a commando sockets on them, and then 16a plugs on the ovens. I know the ovens will not exceed 16a and will be unlikely to even exceed 13a as I won't be using the grill element, I assume there is also a reasonable headway included in the 16a rating.

Or... Am I overthinking this and could make it even simpler by just plugging them into standard 13a sockets on two seperate RFC's using a 13a plug on each? If it doesn't blow the fuse... and I really doubt it would, is there an technical reason this would not be safe?

It goes without saying that whatever the temp solution, I'll be with the ovens the entire time they're used and would give them a test run ahead of the day.

Thoughts?
Just add two sockets to the existing cooker supply using a pair of 2.5 mm or one 4 mm and plug the ovens in with 13amp fused plugs.
 
By far your easiest and cheapest solution will be to put them on 13A plugs. There's nothing in itself wrong with the 16A solution you suggest (except technically you'd need to have a reducing CPD involved as well down to 16A, so realistically that's a small garage style DB involved too) but it's a lot of work and expense for no real benefit.
Why would the cpd need to be reduced to 16amp with it being a fixed load.
 
Because of the 16a rating of the Commando's.
Out of interest why would that be any different to putting a couple of 16a lights on a 32>2x16a 1ph splitter plugged into a distro at an event? (I checked your profile, I work events/TV/film too!)

I've seen that sort of thing done endless times. Surely so long as the device plugged into each 16a is itself rated 16a or less then there should be no issue? Same as plugging two kettles into a single domestic RFC which would have 32a protection.
 
Thanks both for the replies. Tbh as I was typing the bit about breaking into the existing FCU and adding the 16a sockets I was questioning why exactly I would bother when I could simply plug them in using standard 13a plugs... I know the plugs/sockets are over designed in terms of capacity and I really doubt the actual load will be anything like enough to blow the 13a fuses either.

If it blows the fuse, then that's about the worst that can happen and I'll sort the 16a supplies on the existing cooker circuit.
 
But they feed a fixed load of less than 16 amps
Regs state that each and every component of a circuit needs to be able to cope with the maximum demand that may be put upon it under fault conditions - so in this case that would be 40A of the upstream MCB.
Out of interest why would that be any different to putting a couple of 16a lights on a 32>2x16a 1ph splitter plugged into a distro at an event? (I checked your profile, I work events/TV/film too!)

I've seen that sort of thing done endless times. Surely so long as the device plugged into each 16a is itself rated 16a or less then there should be no issue? Same as plugging two kettles into a single domestic RFC which would have 32a protection.
The distro in question will almost certainly have a 16a MCB/RCBO on the source side - so therefore plugging in a 16a ceeform attached to a 17A rated (at least) cable is indeed no issue. What it's feeding is irrelevant because we fault and overload protect the cable, not the device (that's down to the manufacturer to do).
 

Reply to Temp hooking up a pair of 16a ovens for Christmas day.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K
Hi all, I'm new on here.... I have an existing 32A cooker circuit with a wall switch with 13A plug hole.The manufacturer says the new oven is...
Replies
20
Views
6K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top