jord35davies

Hi,
I've only touched SWA a couple of times and I just wanted to know how the SWA gets terminated at the consumer unit. I know you use glands but how does it get terminated to the plastic consumer unit using the metal sheath as the earth. Are there any special requirements?
 
If it's a cheapo dis board you will have problems, the crappy plastic bends when you breathe on it. 6mm brass bolt thru banjo, earth crimped to lug on brass bolt then carry onto earth bar. Even if it was an m/c dis board you should still do the same.
 
hey have started to wire a hot tub, and the rotary isolator i have used has to have a plastic adapter ring to allow the swa to exit and enter it, meaning i can't earth the armour with a banjo, anyone else have this prob and know ways around it???
 
I take it the piranha nuts are the way forward. Never used them before, will it be able to clamp a 2.5mm swa into a 25mm knock out in the isolator box, and still keep the IP rating of the isolator tho?? cheers.
 
Assuming that the hot tub is single phase and you are using either 2 core or 3 core 2.5mm2 SWA the correct gland should be a 20S (either BW or CW depending whether indoor or outdoor) so realistically you will need to fit a reducer to attach the gland anyway. What make isolator is it?

If it is a three phase hot tub please ignore the above ramblings.
 

Reply to Terminating swa in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock