Discuss testing an extension lead with surge protection in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

L

lish70

Just been doing some testing today including 6 brand new extension leads, first two tested ok 3rd one failed with low insulation resistance of around 0.250m ohms. It was then i noticed that this one had surge protection. Can anyone please explain why this would cause these results and how to get around it.

Many thanks
 
SPD's have an internal electronic filter circuit to protect the applinces plugged in hence the poor reading . BS7671 states the Test Voltage for SPD's can be reduced to 250V DC but the pass is still above 1Megohm
 
Thanks guys all sorted now. All makes perfect sense. Still trying to get to grips with my Metrel MI3304 (wish i'd got something smaller!). I've now worked out how to test with the 240v dc :eek:)
 

Reply to testing an extension lead with surge protection in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
463
Hi all, I can't understand why but I always get a small (minimum 0.06mA) earth leakage reading on extension leads (even without surge...
Replies
4
Views
3K
Hi guys and gals, I have a question about the leads to computers (commonly known as kettle leads). I am new to PAT testing so please bear with...
Replies
0
Views
941
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
990
I had a fault finding job on Thursday, intermittent RCD tripping. 2 actually, there was a 30mA RCD upstream, and a 30mA RCBO protecting the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock