Discuss Testing SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

Sparkydan

Does anybody know what table in the regs gives the size of armouring in mm when using the SWA as a CPC ? so i can write this in the circuit details on the installation cert.
 
as far as i'm aware you are not supposed to rely on the armourings for the earth connection of SWA for installations. if there is no provision for earth in the cable you have run then you should run a seperate earth along the length of cable.
 
Agreed,
it is good practice to wire the armour into the earth each end for additional protection, but you should use a core cable for the "proper earth"
Randyrat:D
 
evening all,,,

although I always use an additional core for earth I always thought that you could use a 2core swa and then the armourings as the cpc...

when I use saw I use three core for single phase supplies and also earth the armourings at the supply end for additional protection.

as for where in the books you find the csa of armourings etc I havnt a clue.....
 
on that note, would you need to bond both ends of the bandjo if you were using a 3 core swa with one core being the earth? or just the one end?
 
if you aren't familiar with SWA, then some things to consider

depending on what you're connecting the cable to at both ends, if it's a plastic/PVC enclosure then make sure you earth from the banjo (little brass ring with a smaller brass ring) to somewhere suitable in the CU or enclosure, if the CU or enclosure metallic i like to use serrated washers to give a good connection between the gland and the metallic enclosure.

a factory unit i stripped out the other day only had 4 short lengths of SWA supplying some 3 phase outlets, i didnt need to get my adjustable spanner out of my box, i got every single gland off by hand!! so what i'm saying is, make sure your glands are tight.

i would imagine that street ligthing tends to be mettalic throught, and i imagine that the armourings bonded to the frame of the lighting would be considered adequate

the steel armourings of SWA are notoriously rubbish at withstanding the elements, if everything isn't sealed of or shrouded properly and water gets in the armouring will only last a few short years before it seriously degrades. rotten armourings = high resistance = tripping times will suffer.
 
Last edited by a moderator:
If the swa has three cores and one is used as an earth then it should be banjo'd at the SUPPLY end. If the cable was damaged or cut then the live side would still have protection, kind of.

However, nothing wrong with doing both ends.

You are permitted to use the swa as an earthing conductor, provided various conditions in the regs are met, and obviously both ends are banjo'd, although personally i wouldn't use this method.

You can check the cable manufacturers web site for the CSA's of the armour of the type of cable you used.
 
Last edited by a moderator:
as far as i'm aware you are not supposed to rely on the armourings for the earth connection of SWA for installations. if there is no provision for earth in the cable you have run then you should run a seperate earth along the length of cable.


So what happens if you cut though thw SWA underground??

You can potentially cut though without causing a Fault. The Armour is designed to be used as the MAIN CPC for SWA - so that in the event of it being cut/damaged from any side there will be a fault to earth and therefore trip the MCB/RCD. (Hence why there is no specific CPC ran in a SWA cable).

Where possible i always use a spare core as a cpc aswell (double protection) but in many cases just use the Armour of the SWA.
 
NO NO NO - i believe you are very wrong there!

the armouring is not designed to be relied on as an earth connection!

the armourings reason for being there is to offer mechanical protection, end of - the earth connection is a benefit. the armourings are there to try and protect the cable from being cut through, which is why you use ARMOURED cable! armour is armour, earth is earth
 
This is from the nic eic technical manual

"Whilst the primary function of the metallic armouring of an armoured cable (Fig 1) is to provide overall strength, it may be used as a circuit protective conductor (cpc), main protective bonding conductor or, where practicable, an earthing conductor.
Whichever of these three functions is to be performed by the armouring of a cable, all the relevant requirements of BS 7671 need to be satisfied. The armouring of a cable may be used for more than one of the functions if all the appropriate requirements for each function concerned are met."
 
i'm not saying it can't be used, it is (i believe) good practice to ensure if there is no core to be used as an earth then a seperate earth will be run. the csa of the armourings meets the requirements of the regulations (unless you start using single cores or two core SWA with conductor CSA's of greater than 120mm)

whilst it may be adequate on installation, with 5 years of degredation (depending on the environment) it could easily break down/rust at the glands or any breaks or water ingress into the pvc sheath.

if it's possible i'd always run a seperate earth, and it is in most circumstances i think reasonable to do so

contract i'm on has swa from 2.5 2c upto 185 4c & 800mm 1c, only 3 cables have seperate cpc all of them are 50mm 4c
yours benji

4 core 50mm SWA, the armouring (according to table 54G) is 122mm, where the minimum requirement would be 56.4mm, well within the requirements

i would personally still run a seperate earth, or the best idea is to always run SWA with enough cores for the provision for an earth conductor
 
Last edited by a moderator:
I take your point, but if you run a SWA underground (say 3 core and each core is used as a line conductor) and someone goes though that with a saw, (seen it a few times when people have foundations dug out for a conservatory) then that cable will still be live, not trip the Protective device and becomes a hazzard to the poor bugger you grabs the end of it (if not already had a shock from saw). Where as if the Armour was earthed then the protective device would trip preventing the risk of shock.

The seperate earth would only provide an earth at the other end, but so does the armour. if the ends are terminated properley then there shouldnt be any moisture ingress, and the cable (inc earth continuity) should has as long as the installation
 
What if , right, you've already got 50m of 2 core and you've promised to do your cousins garden lights cheap? If you're worried about degradation , WD40 doesn't hurt on the armour, a liitle bit of mastic etc. And you would have to be especially gifted to cut through the armour enough to give you an earth free path to a live conductor without getting enough earth path through your spade or is it ceramic? I'm only messing!!
 
What I have been doing, and has been accepted by many companies I've been testing for, is I write "SWA" in the cpc column of the test sheet instead of a conductor size.
In the cable type coloumn I write "F" for PVC/SWA or "G" for XLPE/SWA.

It is good practice to use a 3 core SWA now and utilise one core for a cpc, but I dont think there is anything wrong with using the armouring of a 2 core cable for a cpc as long as it is fit for purpose, ie check old cables for signs of excess corrosion.

If someone was to cut the cable, and the blade was to go through the armour into the live conductor first before going into the cpc a dangerous situation would occur. So you need to bond the armour of a 3 core cable to provide the earth path, even if your not using it as the actual cpc.
 
I take your point, but if you run a SWA underground (say 3 core and each core is used as a line conductor) and someone goes though that with a saw, (seen it a few times when people have foundations dug out for a conservatory) then that cable will still be live, not trip the Protective device and becomes a hazzard to the poor bugger you grabs the end of it (if not already had a shock from saw). Where as if the Armour was earthed then the protective device would trip preventing the risk of shock.

The seperate earth would only provide an earth at the other end, but so does the armour. if the ends are terminated properley then there shouldnt be any moisture ingress, and the cable (inc earth continuity) should has as long as the installation

you've got this totally wrong mate, the armouring MUST have a good connection to earth, through the glands, which, if not connected directly to earthed metalwork, then you are required to ensure continuity must be maintained by using a brass banjo. (I also like to use serrated washers to dig into any metal casing to give a good connection).

what the discussion is about is; wether the armourings can/should be relied on for the only means of earthing, armourings and the glands can be considered exposed conductive parts which also requires they be earthed regardless.

also you quoted "if the ends are terminated properley then there shouldnt be any moisture ingress"

shrouds are not always perfect, and if connected outdoors any bangs or bumps could expose the armourings to the elements. but the consideration should not just be fo the ends, what you'd have to consider is, if someone did give the cable a clout it doesn't always take a lot to remove a bit of the sheathing, the tiniest nick could let in water and cause the armourings inside to deteriorate. i've changed loads of SWA which have had water ingress regardless of how good the connections were at the gland
 
I'm with the flukey dude. you can only do an install to the best of your ability. you have no way of knowing what some eejit is going to come and do to your lovely tidy install. If the book says "yes" then someone else has made the decision of wether it's acceptable or not. Obviously a bit of common sense needs to be applied. !
 

Reply to Testing SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
531
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock