Does anybody know what table in the regs gives the size of armouring in mm when using the SWA as a CPC ? so i can write this in the circuit details on the installation cert.
Discuss Testing SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
as far as i'm aware you are not supposed to rely on the armourings for the earth connection of SWA for installations. if there is no provision for earth in the cable you have run then you should run a seperate earth along the length of cable.
contract i'm on has swa from 2.5 2c upto 185 4c & 800mm 1c, only 3 cables have seperate cpc all of them are 50mm 4c
yours benji
I take your point, but if you run a SWA underground (say 3 core and each core is used as a line conductor) and someone goes though that with a saw, (seen it a few times when people have foundations dug out for a conservatory) then that cable will still be live, not trip the Protective device and becomes a hazzard to the poor bugger you grabs the end of it (if not already had a shock from saw). Where as if the Armour was earthed then the protective device would trip preventing the risk of shock.
The seperate earth would only provide an earth at the other end, but so does the armour. if the ends are terminated properley then there shouldnt be any moisture ingress, and the cable (inc earth continuity) should has as long as the installation
is it possible to cut live 300mm swa cable?:
NO NO NO - i believe you are very wrong there!
the armouring is not designed to be relied on as an earth connection!
the armourings reason for being there is to offer mechanical protection, end of - the earth connection is a benefit. the armourings are there to try and protect the cable from being cut through, which is why you use ARMOURED cable! armour is armour, earth is earth
i'm not saying it can't be used, it is (i believe) good practice to ensure if there is no core to be used as an earth then a seperate earth will be run. the csa of the armourings meets the requirements of the regulations (unless you start using single cores or two core SWA with conductor CSA's of greater than 120mm)
whilst it may be adequate on installation, with 5 years of degredation (depending on the environment) it could easily break down/rust at the glands or any breaks or water ingress into the pvc sheath.
if it's possible i'd always run a seperate earth, and it is in most circumstances i think reasonable to do so