Hi guys, a bit of advise needed if you can help. So i was doing an EICR at a family members property they own and rent out. Its an older property with only a socket or 2 in each room. I could see straight away that the sockets were all overloaded with heavily filled extension leads with double plugs etc

So i ran continuity, R1 + R2s, Ze, PFE, Zs tests with no issues. I started to run the Insulation resistance tests @ 250v which most circuits passed with no issues apart from the Ring Main Sockets which. I got a >999 for Neutral to Live but I got a low reading of 112 ohms for Live to Earth. For 500v I got a measurement of 600 ohms Neutral - Live and 120 ohms for Live - Earth. A couple of the other circuits also struggled at 500 volts. I measured connected to earth bar so not sure if i should go back and measure the cables direct to see if that helps.

What would your thoughts be on the matter. Rewire? for the sockets at least? Or any suggestions. Maybe I'm missing something, i mean i don't know everything (Every day is a school day :) )

Hate the thought of saying to the family member that they need to spend money on a rewire but i know i need to think of Safety first.

Cheers Guys

Andy
 
Very different results at 250v and 500v with N > L suggests a surge protected extension lead plugged in which sounds plausible from your post.
Was also going ask about units, as 120 ohms is roughly 2 amps current (230v/120 ohms)- instant RCD trip (if there is one).
I was thinking this but wouldn't i have got a low result with the 250 volts? I mean i asked the tenant where every plug was so i thought we cleared them all. Bloody nightmare EICRs when you have messy tenants

I appreciate the reply.

Andy
 
Hi guys, a bit of advise needed if you can help. So i was doing an EICR at a family members property they own and rent out. Its an older property with only a socket or 2 in each room. I could see straight away that the sockets were all overloaded with heavily filled extension leads with double plugs etc

So i ran continuity, R1 + R2s, Ze, PFE, Zs tests with no issues. I started to run the Insulation resistance tests @ 250v which most circuits passed with no issues apart from the Ring Main Sockets which. I got a >999 for Neutral to Live but I got a low reading of 112 ohms for Live to Earth. For 500v I got a measurement of 600 ohms Neutral - Live and 120 ohms for Live - Earth. A couple of the other circuits also struggled at 500 volts. I measured connected to earth bar so not sure if i should go back and measure the cables direct to see if that helps.

What would your thoughts be on the matter. Rewire? for the sockets at least? Or any suggestions. Maybe I'm missing something, i mean i don't know everything (Every day is a school day :) )

Hate the thought of saying to the family member that they need to spend money on a rewire but i know i need to think of Safety first.

Cheers Guys

Andy
Had you unplugged everything before you started testing IR
? what MFT are you using. parallel earth paths may be a clue, were there any hard wired load ie boiler or heaters in circuit when you tested, what were you testing L /E N\E L/N? Daft question but was the power OFF and isolated? was the Main Earth dissed from the MET,was the test a global test?
 
I was thinking this but wouldn't i have got a low result with the 250 volts? I mean i asked the tenant where every plug was so i thought we cleared them all. Bloody nightmare EICRs when you have messy tenants

I appreciate the reply.

Andy
EDIT - you said >999 Mohm L-N at 250v and 600 ohms L-N at 500v didn't you. So that does fit. The surge protector probably kicked in. For now I'd forget this and focus on the L-Earth which is concerning.

The hard thing is deciding when it just becomes FI and a new piece of work.
I'd probably do two more things as part of an EICR -
1) Remove cpc's from earth bar and try again.
2) Then break the ring somewhere and test each leg.
If same with cpc's removed (so it's a local circuit issue) and if one leg is clear you at least have a clue it's solvable.
Might just be socket screw chafing/touching a live.
 
Last edited:
EDIT - you said >999 Mohm L-N at 250v and 600 ohms L-N at 500v didn't you. So that does fit.

So it really is that bad. Wow.
The hard thing is deciding when it just becomes FI and a new piece of work.
I'd probably do two more things as part of an EICR -
1) Remove cpc's from earth bar and try again.
2) Then break the ring somewhere and test each leg.
If same with cpc's removed (so it's a local circuit issue) and if one leg is clear you at least have a clue it's solvable.
Might just be socket screw chafing/touching a live.
Cheers for the advice. Really appreciate it. I'll go back and try what you suggested.

Andy
 

Reply to Testing Thoughts in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
757
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
644

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock