The other option, although not ideal, is to test and record that Ze was taken with parallel paths in place. This happens more so in commercial and industrial settings where the supply cannot be shutdown for financial reasons.

That is not Ze, that is a Zs measurement.
[automerge]1592940600[/automerge]
That's what I would have expected to be done. Although would it really be necessary to connect all three of the original wires that now just go back to the cut-out? Surely one would be enough and the other two, now redundant, wires could be cut back flush.

Every time I have come across this it has dated back to the days when 6mm main bonding was installed so all 3 conductors are 6mm.
Now the conductor from the service cutout to the MET should be 16mm for a PME supply (which this is as per the label)
So if they are 6mm then all 3 would need to be connected to achieve the ideal 16mm CSA.
 
If I remember from my college course many moons ago, you can also request the Ze figure from your local, friendly and ever helpful electricity supplier.
I've never tried it though. Anybody else had success with this?

They will give you their nominal design limits, which are usually also available from their websites (buried somewhere, if you look hard enough)
For example 100A TNS will normally be quoted as 0.8ohm
100A TNCS will normally be quoted as 0.35ohm for existing supplies or 0.25ohm for new supplies (this is true for UKPN at least, not sure if the others work to 0.25 now/yet)
 
Yes. Those (IIRC ) are the standard figures from DNO Engineering Recommendation P23/1 - which, I believe, is the origin of the 0.35 and 0.8 figures.
 

Reply to Testing Ze when you cannot disconnect the bonding? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
776
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
TT System with 31 ohm ze that drops down to 0.31 ohms when the bonding is all connected Am I right in thinking that's because a house nearby has...
Replies
9
Views
2K
Hi, I've had an unusual result from taking a Ze at a clients house and wondered what everyones take on it would be: The property is TN-C-S A Ze...
Replies
9
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock