Jon_

-
Reaction score
1
Could you tell me whether most of the tests carried out for a Domestic Electrical Installation Report would have to be repeated if a replacement consumer unit is subsequently fitted?
 
Could you tell me whether most of the tests carried out for a Domestic Electrical Installation Report would have to be repeated if a replacement consumer unit is subsequently fitted?
If it was you who carried out the EICR a few days previous I would use the same reads, however I would redo Zs and obviously any any new residual current device tests.
 
Yes. Continuity of cpcs/ring final conductors/ main protective bonds, insulation resistance, polarity, Ze/Zs, rcd/rcbo tests.
 
Could you tell me whether most of the tests carried out for a Domestic Electrical Installation Report would have to be repeated if a replacement consumer unit is subsequently fitted?
Look at Best practice guide no 1 for a CU change
Earthing and bonding continuity
Global IR test need L/N to Earth is acceptable
RFC continuity
Polarity
 
Last edited:
I'd retest ze, ring continuity, zs for each circuit and obviously any new rcds. If you feel you have to retest insulation then something has gone very wrong with the new install.

That being said, if someone else had done the eicr I'd do a full retest. Some EICR's are tested using eyeballs and imagination, not test meters!
 
Full test IMO is the only way. On old houses needing a CU, it's normal to find lots of faults. Open rings, reversed sockets, no CPC, borrowed neutrals, nails in cables, no bonding, inadequate earth, mice...Just so many problems... I have spent a week doing CU on 2 bed houses before.
It pays to spend long enough beforehand to tell customer up-front what to expect, then build that into quote with a further contingency for unknown faults . I tend to try to do 80% of the tests with the old CU in place, ideally the day before. Also get all major faults fixed then, because once new CU is in, you'd have otherwise A) connected in faulty circuits, or B) maybe lost the will of the Customer to pay more, since they see the shiny unit and assume it's done. -Puts you in a spot.
Doing it up-front means that where it's really bad, I can tell them without first having destroyed the old set-up. Basically an EICR every time, but without the paperwork (since that's all built in to the subsequent EIC ). Working alone, where circuits need extending (really common), new tails/EC/bonding etc (really common) , and faults fixed (nearly always necessary, sometimes taking ages..), there's just not enough hours in a day to do it all and switch it on the same evening knowing it's safe. - It's just not worth the risk of getting caught short at 9PM after a tough twelve hour day.
I nearly never do a CU in 1 day, and only connect one in when I am 80% sure of all the tests results already, making finishing the testing and sealing possible the same day.
 
Good post @1Justin - I spent 4 hours testing an old installation and noting my readings then labelling in order to have an easier time of changing the CU this week. Left it working with a couple of circuits, that didn't need to be on there to function, disconnected until new CU.
I don't think that many things are as quick as you think they will be, double the time you think and you'll be closer.
 
Honestly guys, absolutely nothing. We've got another druggie ----- living next door again, she phones the police regularly with stories about being attacked or threatened. This time she told them that someone had tried to kick in the back gate overnight.
I know most of the local shift by name, they've been back & fore for 3 years,
So they come to ask if anything has happened each time or is it just another story.
 
Honestly guys, absolutely nothing. We've got another druggie ----- living next door again, she phones the police regularly with stories about being attacked or threatened. This time she told them that someone had tried to kick in the back gate overnight.
I know most of the local shift by name, they've been back & fore for 3 years,
So they come to ask if anything has happened each time or is it just another story.
Nice neighbors then?
 
Wonderful mate, first 4 years the neighbours were brilliant.
Since then we've had a Fake hardman, Drug dealer dealing from there, Druggie prostitute than ran her trade from there.
Druggie car thieves (Police there daily, 7 times new years eve) & now this druggie lunatic.
Anyone got any Semtex ?.
 
Wonderful mate, first 4 years the neighbours were brilliant.
Since then we've had a Fake hardman, Drug dealer dealing from there, Druggie prostitute than ran her trade from there.
Druggie car thieves (Police there daily, 7 times new years eve) & now this druggie lunatic.
Anyone got any Semtex ?.
I mean that's gotta be pants, worst I got is my neighbours security light going off all hours, I and I installed it :(
 
There's no button @Specialist to explain how we feel. Hope it settles down. A gentlemans home should be his castle but you shouldn't have to use the fortresses just to live your life. Ear plugs and bed (just like the missus)!
 
There's no button @Specialist to explain how we feel. Hope it settles down. A gentlemans home should be his castle but you shouldn't have to use the fortresses just to live your life. Ear plugs and bed (just like the missus)!

Thanks Buddy, I appreciate your thoughts. These skanks have the Police tied in knots at the minute, they're apparently housed under the Mental health protection act & have Social services on their side.
Appears they can pretty much get away with just about anything, Police arrest them then the taxpayer forks out for lawyers.
Had a gentle warning from the Police not to do anything to them, if I do then CPS won't hesitate to prosecute.
I just love the fairness of the British justice system.
 
Last edited by a moderator:
Head up. We're better than all these scum. They'll be moved on soon, or OD or something. keep your head screwed on and buy some blood ear plugs as said earlier :)
 
Head up. We're better than all these scum. They'll be moved on soon, or OD or something. keep your head screwed on and buy some blood ear plugs as said earlier :)

You know what mate Your right, we are better than this scum. Can't keep my head screwed on though, lost my sanity years ago. I became a sparky :). Nah only joking, I've loved most of it ;):D
 
Fair point. We chose our level of sanity by getting into this business. Maybe set the bar low, but at least we chose the height and went for it. Could have been a wreck head or a bricky!
 
You know what mate Your right, we are better than this scum. Can't keep my head screwed on though, lost my sanity years ago. I became a sparky :). Nah only joking, I've loved most of it ;):D

Keep ringing the cops, every time they step out of line, get your neighbours do the same. It will pee off the local Super'Nintendo, when he conducts his/her morning prayers. Same with your local council. Whilst the authorities are probably doing the best they can, the constant barrage of complaints, will be just too much for them. Write to your local MP as well.
 
Keep ringing the cops, every time they step out of line, get your neighbours do the same. It will pee off the local Super'Nintendo, when he conducts his/her morning prayers. Same with your local council. Whilst the authorities are probably doing the best they can, the constant barrage of complaints, will be just too much for them. Write to your local MP as well.
Or you give this bloke a call
 
Thanks again for the support guys, we actually had a reasonably quiet night last night.
Once the Police & Ambulance went, only had 1 more Police attendance at 4.20 am this morning.

The police to be fair to them have been excellent, they keep coming out & nicking them but then they get let back out.
The biggest problem is the landlord, the Police & our local Councillor go through the long process of getting the scum evicted.
Then 3 to 4 days later the landlord shoves another lot in & it starts over again.
Local council reckon they can't do anything because it's a private rental property.
 

Reply to Tests for replacement consmer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Replies
18
Views
382
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Replies
2
Views
409
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
727
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock