Discuss The maximum value for Zs on a TT system is 50/I delta. So for a 30mA RCd is 1667 ohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

because with TN earthing, the Zs should be < Zs(max.) for the OCPD, whereas with TT this is not usually possible, so you are relyingon the RCD for fault protection rather than the OCPD.
 
strange that before the advent of RCDs, when the main earth was from the incoming lead water supply, we had Ze values way below what was achievable with a rod. now this is banned.?????
 
Yes but they installed a voelcb for TT installations before rcd’s but I’ve never witnessed a low enough Ze off a water pipe personally.
Maybe because they were all changed to plastic at some point we can’t rely upon water pipes unless a private supply and care is taken against its alteration and removal
 
strange that before the advent of RCDs, when the main earth was from the incoming lead water supply, we had Ze values way below what was achievable with a rod. now this is banned.?????

That's because they're ripping these pipes out and using PVC instead. So they can no longer be relied on.

Me, I've only ever installed rods in quarries, and I had the blast shot drilling rig to bore me some nice 30m deep holes. A 30m rod, back filled with bentonite in a saturated limestone table. Sub 1 ohm was real easy to achieve. Especially for new substations where 4 to 6 of these rods were connected around the perimeter.

Not exactly feasible at someones terraced house.
 
Morning all. Have I misunderstood this thread? RCDs are fine for fault protection:

411.4 TN system
411.4.5 The following types of protective device may be used for fault protection:
(i) An overcurrent protective device
(ii) An RCD.
 

Reply to The maximum value for Zs on a TT system is 50/I delta. So for a 30mA RCd is 1667 ohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Does a RCBO protecting a single circuit mean it can have a maximum Zs of 1667 Ohms since it's being used as fault protection?
Replies
3
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock