on a TN installation, the Zs values should be compliant with OCPD disconnection times, if you've not made a cock-up of the design. using RCDs as a "get out of jail" card is, IMO, sloppy,unprofessional, and just lazy. leave that shyte to the septics with there GFD crap .
 
Telectrix, what you've just said directly contradicts the reg I quoted above. Can you back it up with another regulation please?

Bear in mind disconnection times only apply to earth faults, not short circuits
 
Telectrix, what you've just said directly contradicts the reg I quoted above. Can you back it up with another regulation please?

Bear in mind disconnection times only apply to earth faults, not short circuits
a RCD should only be used for fault protection where the Zs values exceed those in tables for each OCPD. e.g. in a TT system where the Ze is too high to achieve compliant figures. RCDs that are not regularly tested have been known to stick.' sometimes an unnoticed N-E fault will prevent the RCD from tripping. i would not rely on one for fault protection unless absolutely necessary.
 
That's true, RCDs can stick, however, they can and should be tested, and replaced if faulty. The same cannot be said for MCBs - we only have blind faith that they will do their duty when the times comes. I understand that MCBs are manufactured to be more reliable, but you see my point?

The IET are fine with us using RCDs as fault protection - the max length tables for standard circuits in the OSG have columns of longer values specifically for RCD protected circuits on TN systems
 
maybe old school, but been brought up before RDCs were even invented. back in the 70's , local DNOs were converting to PME so as to ensure disconnections as used to be called eebads, now ads. before then a fault could take a fortnight to diss supply. not good if you got a live -earth fault.
 
Agreed, it would imply that something is seriously wrong somewhere. However, it does mean, all other things being correct, that lazy types like me can ignore max disconnection times calculations
slippery slope. do you then ignore the lack of cpc's to metal fittings, sockets close to a bath, andonandonandon.
 

Reply to The maximum value for Zs on a TT system is 50/I delta. So for a 30mA RCd is 1667 ohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Does a RCBO protecting a single circuit mean it can have a maximum Zs of 1667 Ohms since it's being used as fault protection?
Replies
3
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock