I'm doing a garage conversion. 70mm insulation on block then an inch gap battened on top, then 35mm insulating board. Where's best for the cable to go in terms of derating etc...
Cheers.
 
probably on top of the lower insulation so there's a 1" airspace above. what is the cable/s feeding?
 
This is on the walls so feeding everything.
ELEC htrs, shower, water htrs, lighting power
. Just think that gap will be the warmest place?

The gap may be warm and you'll need to factor this in to your cable sizing calculations, but you need to avoid putting holes through the insulation as much as possible to avoid compromising it so in the gap is probably the best place for the cables.
 

Reply to Thermal insulation covering cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm about to reroute cables and sockets/switches from the ceiling down to the socket height after insulating a wall. I understand this will...
Replies
2
Views
199
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
269
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K
Hi, The current carrying capacity tables in the BS 7671 for twin and earth cables are only for buildings that have thermal insulation. I'm...
Replies
48
Views
5K
I’d appreciate your professional views on this question, as I’ve had 2 of the associated electrical bodies quizzed on this.!!!! ON changing/up...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock