NICK C SPARKS

Hi all just installing a 3 p extractor fan and in the instructions which are in broken english it says it needs thermistor protection would this just be wired back to the dol starter and wired in line with the contactor circiut ai through the thermsitor relay( which i presume is normanly closed) them to the motor and back to a2 cotactor terminal
cheers
 
Actually, it depends on the thermistor. Some go open circuit when a certain temperature is reached and some are resistive that change resistance with temperature and need a special thermistor relay that has to be reset.

To be honest, I rarely see them connected at all (especially in fans as by their very nature they blow cool air over themselves) As long as the overload is set exactly right - they'll trip if a problem occurs.
 
The fan won't be blowing cool air over the motor, the fan is being used in an extraction situation the air will more than likely be very warm and humid
 
Actually, it depends on the thermistor. Some go open circuit when a certain temperature is reached and some are resistive that change resistance with temperature and need a special thermistor relay that has to be reset.

To be honest, I rarely see them connected at all (especially in fans as by their very nature they blow cool air over themselves) As long as the overload is set exactly right - they'll trip if a problem occurs.


You are talking of thermal fuses not thermistors. They are only used in small cheap motors.


Thermistors and thermocouples are embedded in the windings of many large motor to protect the huge investment companies sink in to them.
 

Reply to Thermistor protection in 3 phase star wired motor in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock