Hi all just installing a 3 p extractor fan and in the instructions which are in broken english it says it needs thermistor protection would this just be wired back to the dol starter and wired in line with the contactor circiut ai through the thermsitor relay( which i presume is normanly closed) them to the motor and back to a2 cotactor terminal
cheers
 
The two leads from the thermistor wire direct to the relay. The relay will have both NO/NC contacts that you can wire in to the DOL starter to suit you.
 
Actually, it depends on the thermistor. Some go open circuit when a certain temperature is reached and some are resistive that change resistance with temperature and need a special thermistor relay that has to be reset.

To be honest, I rarely see them connected at all (especially in fans as by their very nature they blow cool air over themselves) As long as the overload is set exactly right - they'll trip if a problem occurs.
 
The fan won't be blowing cool air over the motor, the fan is being used in an extraction situation the air will more than likely be very warm and humid
 
I think he's sorted it now. He's had 4 years :) Daz
 
Yeah the similar thread thing has caught me out before!
 
Actually, it depends on the thermistor. Some go open circuit when a certain temperature is reached and some are resistive that change resistance with temperature and need a special thermistor relay that has to be reset.

To be honest, I rarely see them connected at all (especially in fans as by their very nature they blow cool air over themselves) As long as the overload is set exactly right - they'll trip if a problem occurs.


You are talking of thermal fuses not thermistors. They are only used in small cheap motors.


Thermistors and thermocouples are embedded in the windings of many large motor to protect the huge investment companies sink in to them.
 

Reply to Thermistor protection in 3 phase star wired motor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top