Discuss Thoughts needed - Battery back-up in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
41
Iv been thinking about a way to keep the lights on during a power cut and have come up with the following idea, it will be mainly used in domestic properties, iv included an automatic change-over, im picking up a ups today and am going to trial it at home, just wondering if anyone has any thoughts or ideas before i go ahead????

lighting backup.jpg
 
The UPS contains its own transfer relay - why are you duplicating this with an external contactor? That's the whole point of a UPS!

Importantly, you must provide the correct level of isolation between the output of the UPS and the DNO supply using the correct contactor type etc. otherwise it poses a serious hazard to DNO workers in the event of a fault. Wiring some random contactor with an NC contact up to do this probably won't meet the requirements, so if for some reason you need external switching I would suggest buying a turnkey solution that has been type approved for the purpose. But I don't see what purpose it serves.
 
The internal relay only handles switching between ac and battery, the reasons I included a nc no contactor was to allow for automatic switching and to isolate the ups from the ccu in the event of a power cut, it has nothing to do with dno as this setup won't affect any isolation
 
Hi,

I'm with Lucien on this one. A UPS is a UPS and does what it's designed to do. Why the need for a seperate contactor? In the event of a Mains failure the Battery backup would be used for your lighting via the UPS, that's what you are trying to achieve isn't it? Also it gives the correct segregation from the DNO and UPS supplies.

Regards.
 
Agreed with the above,when wiring an UPS you feed your power in and your load comes out so no need for a separate contactor,you will not need this as when the ups lose it's feed and goes to battery mode there is nothing coming back down the feed cable so no danger of feeding back onto the network.If you have an UPS then just try it on the bench and you'll see what we mean.Wiring wise you power the UPS from your CU then remove L N and E for lighting circuit from CU and feed from UPS via a suitable device to give isolation and overload protection E.G a 1 way CU,just remember to isolate at this point when working on the circuit.
 

Reply to Thoughts needed - Battery back-up in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K
Hi All Had an enquiry about installing a generator fed UPS to a house. I have a minimal amount of experience with UPS but am certainly no expert...
Replies
3
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
24VDC Battery Back up - with 2 x 12VDC - 100Ah Batteries - monitor and charge options. 2 x 100AH deep cycle batteries - wired in series. Can I...
Replies
0
Views
745
Hi Looking for some advice please. Keep having issues with flickering lights, some devices such as dehumidifier "stuttering" because power...
Replies
1
Views
830

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock