TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual RCBOs

Required to install three phase circuits for new equipment, is there a better way of doing this than fitting a 4pole RCD ahead of the main switch?

Conscious that this is going to cause total loss of power if a problem ever occurs.

No space nearby to install a seperate DB for the three phase equipment only.
 
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual RCBOs

Required to install three phase circuits for new equipment, is there a better way of doing this than fitting a 4pole RCD ahead of the main switch?

Conscious that this is going to cause total loss of power if a problem ever occurs.

No space nearby to install a seperate DB for the three phase equipment only.
Go from the triple pole circuit breaker into an adjacent DIN rail enclosure with your four pole RCCB.

I assume that there's upstream fault protection, e.g. an S-type RCCB?
 
Go from the triple pole circuit breaker into an adjacent DIN rail enclosure with your four pole RCCB.

I assume that there's upstream fault protection, e.g. an S-type RCCB?
No room adjacent to the distribution board to be able to do this as there are 3 x three phase circuits to install so 3 x RCCBs and enclosures would be required.

No upstream RCD but didn't think this was a requirement of BS7671 if meter tails are visible and proper glands and termination are in place?

Easy enough to add a 100mA time delay RCD upstream of the board if required but would still need 30mA RCCBs for each three phase circuit.

Would an upstream 30mA 4P RCCB be ridiculous?
 
My understanding is that all circuits on a TT system are required to be protected by a 30mA RCD .. is this wrong?

This is indeed wrong.

Installations with TT earthing often cannot guarantee a suitable Zs to be able to meet the requirements for fault protection.
So in order to achieve adequate fault protection RCDs are used.

If an RCD is required for fault protection it does not necessarily need to be 30mA and it may also be acceptable to have a time delay.

All other requirements for RCD protection, additional protection etc, still apply.
 
What is the nature of the 3-phase circuit you are installing?

If it is for a socket outlet up to 32A or buried cables less than 50mm from wall surfaces then it would need 30mA "additional protection", but if not (above 32A sockets or hard-wired) then often not but obviously depends on what it is. Then the use of a something 100mA delay RCD up-front would allow fault protection, but with the risk of everything going off should that happen.
 

Reply to Three phase equipment RCD protection on a TT system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
871
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
Replies
5
Views
4K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
685
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock