Discuss Three phase TT install with distribution circuit and RCBOs in the UK Electrical Forum area at ElectriciansForums.net

Leesparkykent

Esteemed
Reaction score
9,113
I have an Install where a 16mm 4core has been installed previously. ATM the SWA is coiled up either end At the supply which is a barn converted in to an office for the homeowners business and plant room in new extension to the house. There is no PME available as over head, in the middle of no where and in an earlier life was a farm. My intention is to install a 100mA time delayed RCD at the supply in the office mains room and then a fused switch/switch fuse for the distribution circuit. In the plant room at the end the distribution circuit I want to install a 3 phase DB but this is where it gets a little tricky........All the circuits that need additional protection my means of a 30mA RCD will have to be put on RCBOs however I'm struggling to find single pole switched neutral RCBOs. In a single phase installation I would use SBS compact RCBOs as they are single pole switched neutral but SBS don't do three phase DBs etc. Is any one aware of a brand where I could achieve this or think of another idea?
 
This is a proper grey area and I don't think you will get the rcbos you need. I have used single pole on tt before with a 4 pole time delayed up front device the only problem is nuisance tripping from one of the circuits because the neutral is not disconnected. Years ago fuses and mcbs were acceptable on tt systems providing fault protection was maintained and they were single pole. Provided they are not used for isolation I don't see a problem.
 
This is a proper grey area and I don't think you will get the rcbos you need. I have used single pole on tt before with a 4 pole time delayed up front device the only problem is nuisance tripping from one of the circuits because the neutral is not disconnected. Years ago fuses and mcbs were acceptable on tt systems providing fault protection was maintained and they were single pole. Provided they are not used for isolation I don't see a problem.
My problems exactly that neutral earth fault on one of the circuits takes out RCBO and then the up front time delayed RCD. I cant believe I cant seem to find any single pole switched neutral rcbos for a three phase DB.
 
My problems exactly that neutral earth fault on one of the circuits takes out RCBO and then the up front time delayed RCD. I cant believe I cant seem to find any single pole switched neutral rcbos for a three phase DB.
Can you not substitute the triple pole board for three dual rcd boards?
 

Reply to Three phase TT install with distribution circuit and RCBOs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
828
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual...
Replies
15
Views
4K
I may be seeking the holy grail here, but does anyone have any instant thoughts for a compact 3 phase distribution board that doesn't cost the...
Replies
7
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock