Discuss Time delay RCD or Mechanical Protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Okay!

So, I’m looking to plug a knowledge gap.

The set up is a DB in a main dwelling and a second DB in an outbuilding.

The supply from the main dwelling to the outbuilding is 16mm2 split concentric. It is buried in sealed ducting at 1500mm at the deepest point (under the lawn). It comes above ground inside the outbuilding. The other end comes above ground outside the main dwelling between the flags and the gable end. It is protected by a PVC cable guard. The cable is installed in ‘safe zones’ in the outbuilding but less than 50mm deep into the wall (behind plasterboard).

The outbuilding has all circuits protected by 30mA RCBOs.

So, my question. As the cable is not armoured does this cable need RCD protection in the main dwelling from where it originates, and if so, does it need to be 30mA or can it be 100mA and/time delayed, or can it just be put on an MCB?

Thanks in advance.
 
Split concentric would need a 30mA RCD for additional protection, if buried in a wall at <50mm.
Or be otherwise mechanically protected - for example in earthed metallic conduit.
And I assume the RCD would need to be in the main dwelling from where the split concentric cable originates.
 
Never used split concentric but I thought the design was such that anything that penetrates as far as the Live centre core would have to pass through either the Neutral or Earth creating a high current fault path and near instantaneous disconnection.

This is unlike T&E where you can screw directly into the Live without creating a fault path, until someone poor sod touches the screw/mounted equipment.

I know the regulatory requirement but what does an RCD offer with split con?

What other fault scenarios would make the RCD more relevant?

I guess partial penetration, shorting Neutral and Earth?
 
Never used split concentric but I thought the design was such that anything that penetrates as far as the Live centre core would have to pass through either the Neutral or Earth creating a high current fault path and near instantaneous disconnection.

This is unlike T&E where you can screw directly into the Live without creating a fault path, until someone poor sod touches the screw/mounted equipment.

I know the regulatory requirement but what does an RCD offer with split con?

What other fault scenarios would make the RCD more relevant?

I guess partial penetration, shorting Neutral and Earth?
I’d read something like this before I posted.

It would be interesting to see if the split con would negate the need for an RCD. It seems as though doubling up, and with not being able to use a time delay RCD the possibility of the RCD tripping in the main dwelling before the RCBO is likely and that’s a 100m round trip (pun intended) to reset the RCD.
 
Previous editions of the Regulations permitted the use of split concentric without additional rcd protection but it was removed in later editions hence it now requires additional protection.
 
Previous editions of the Regulations permitted the use of split concentric without additional rcd protection but it was removed in later editions hence it now requires additional protection.
Would be interesting to know the reasoning behind that change, are you aware of any articles?
 
What is the earthing arrangement? TT or TN?
If it's TT it would need some form of fault protection even if mechanically protected.
 
Would be interesting to know the reasoning behind that change, are you aware of any articles?
No I will try and find it later in some old Regs. I believe the reason is the live conductors is not totally surrounded by an earthed conductor, some of it is neutral as this pic shows.
 
If, as it now seems to be the case, it would need 30mA additional protection due to being < 50mm behind walls then adding physical protection (either thick steel to prevent penetration, or earthed metal trunking to guarantee disconnection like SWA armour) would be the best option to avoid the lack of RCD selectivity.

More so if the outbuilding has a few circuits and lots of electronics so total leakage could well be creeping up to 15mA+ and a risk of nuisance tripping without any fault.
 

Reply to Time delay RCD or Mechanical Protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
So as the title says can I use a mcb as the main switch. Basically to keep it short I’ve took a 25mm sub main to power an outbuilding. Mains...
Replies
11
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
855
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock