OK I'm prepared for the usual onslaught so here goes...

I recently bought a clamp meter Uni-T UT210E.
The first thing I did was check it out against my trusted AVOs and also a couple of other cheapo DMM's, (measure current through wire through probes and compare to clamp reading). The clamp is more accurate than I expected even at low currents (milliamps) or at least mostly the meters all agree with each other (although they could all be wrong!)
So in the spirit of playing with my new toy I thought I'd see how my power monitoring meters stood up. I suspected they were under reading, they are. I never believed them at low power anyway and
as consumption increases the discrepancy reduces considerably as you would expect but not too bothered about this as there is no means of calibration anyway.

I also measured around the earth cable which is connected from the cutout to the main earthing block, expecting to measure almost zero, but the reading was higher than I expected - (no clues given here as looking for real world earth return figures and opinions). What figure would you typically expect?

Caveat: I admit I didn't isolate everything I should/could have (I had to avoid incurring the wrath of SWMBO, and so I will be repeating test at a later date ) Consequently there were a few 'elderly' earthed appliances which could have had some bearing by leakage or induced currents, but no lights on, led or otherwise.

Opinions gratefully received.
 
On industrial installations we sometimes see > 20Amps earth current but I'd expect a domestic installation to be less than an Amp.

With a TNCS earthing arrangement you should do the same test with the power switched off at your CU. The current you're seeing probably isn't all from your installation.
 
On industrial installations we sometimes see > 20Amps earth current but I'd expect a domestic installation to be less than an Amp.

With a TNCS earthing arrangement you should do the same test with the power switched off at your CU. The current you're seeing probably isn't all from your installation.

Good point- thanks, will do when circumstances allow.
 
Interesting experiment :)
Domestically I expect to see only a few mA per circuit. The domestic additional protection RCDs will trip somewhere between 15mA and 30mA of earth current.
If I may ask - do you have metal gas and water pipes ?
 
Last edited:
Interesting experiment :)
Domestically I expect to see only a few mA per circuit. The domestic additional protection RCDs will trip somewhere between 15mA and 30mA of earth current.
If I may ask - do you have metal gas and water pipes ?

Thanks, yes, both metal.
It may be a while before I can de-energise all and measure again.
 
Agree with Marvo, there can be all sorts of external circulating currents from your main EB passing through the EC, that's a fact of life with TN-C-S and one of the reasons larger bonding cables are specified. You might see anywhere between zero and tens of amps under normal conditions, there are so many variables it's hard to predict. In any case it bears no direct relation to your leakage current, in fact if you put heavy load on you will probably find it correlates more with the load current.
 
Interesting experiment :)
Domestically I expect to see only a few mA per circuit. The domestic additional protection RCDs will trip somewhere between 15mA and 30mA of earth current.
If I may ask - do you have metal gas and water pipes ?
I forgot to add that of course the RCD won’t trip unless it measures a L/N imbalance, irrespective of earth leakage (unless the leakage is causing the imbalance) ...apologies for stating the bl**din’ obvious!
 
The imbalance is the earth leakage, they are the same thing by definition (at least for all practical purposes). It's the earthing conductor current that is a different kettle of fish and that is what you are measuring here. It consists of the small leakage current from your own installation (that the RCD can detect, as it results in a differential current in the circuit) plus any currents passing to extraneous parts via both the bonding and CPCs. Although the latter are only driven by low voltages, typically the few volts of drop along the distribution and service cables, they are passing through a very low loop resistance maybe of fractions of an ohm, so the currents can dwarf the leakage current by orders of magnitude.
 
The imbalance is the earth leakage, they are the same thing by definition (at least for all practical purposes). It's the earthing conductor current that is a different kettle of fish and that is what you are measuring here. ....
Thanks, yes perhaps I didn't put it well but that was precisely the point I was trying to make - that extraneous current measured on the earth conductor is not necessarily the result of L/N imbalance in the property.
 

Reply to TN-CS main bonding cable typical leakage current question. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Hello. I'll apologize to start with as due to my lack of knowledge on the matter I'm likely to waffle a bit and call everything by the wrong name...
Replies
16
Views
2K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock