No thats not what i mean , forgot war and all that. Why is it that a in one house a tncs system here can be connected to neutral but in another house it cant?
because where PME is provided, the supply has the N (star point) reliably earthed at several points along it's route. therefore, it's maintained at ground potential. best option is to TT it with RCD for fault protection, as wilko stated .
 
The OP specifically said the link would be in the bus bar, which on the boards I've worked with would be before any RCD. That way fault current returns through the neutral and through the RCD as normal current would, and the RCD would not operate.
Yes, creating the link at the busbar, or anywhere down stream from the RCD would cause the RCD to trip whenever power was used.
 
Okay, so the scenario in the OP was that a link was made between the earth and neutral bus bars. This is my interpretation of that, as depicted by the purple line. (Apologies about the Paint job, not quite Richard Burns spec).

OP said:
My question is Whether or not i could create a link between the Neutral and Earth bar to create a tncs system

So current flows through the line through the RCD, and out on the first circuit. There's a fault, and it returns via the earth path. The earth path is linked to neutral before it passes through the RCD, and the current then passes through the neutral via the RCD. The RCD wouldn't see a fault and doesn't operate.

View attachment 35580
 
You won't get to the fault stage, as the RCD will operate as soon as any power is used.
Some of the return current will return to the power supply via the earth instead of via the neutral.
The RCD will see the imbalance between the Line and neutral and trip.
 
You won't get to the fault stage, as the RCD will operate as soon as any power is used.
Some of the return current will return to the power supply via the earth instead of via the neutral.
The RCD will see the imbalance between the Line and neutral and trip.
What earth? There is no earth, it has been linked to neutral to create a bodged TNCS
 
You've only got to think of the scenario of wrong neutral leg to wrong neutral bar or when you're working on a circuit switched off at the board but neutral not removed, so easy to trip if neutral and earth touch. The amount of imbalance needed through the RCD coils is minuscule to cause a trip. No way would the install be a happy install if @hightower 's scenario was attempted.
 
You've only got to think of the scenario of wrong neutral leg to wrong neutral bar or when you're working on a circuit switched off at the board but neutral not removed, so easy to trip if neutral and earth touch. The amount of imbalance needed through the RCD coils is minuscule to cause a trip. No way would the install be a happy install if @hightower 's scenario was attempted.

I'd argue quite the contrary - it would be too happy, and would render the RCD completely useless.
 
It's electrickery, it knows more than us! We're just wire monkeys! I understand your passion though - we need a "myth buster"
 
Hi - not wishing to step into a hole, but would not the luckless chap be standing on the earth and the earth fault current flow through him? This would unbalance the RCD in the usual way, if it had ever been able to stay on line to begin with as per Spin #45 and Rpa #47 thoughts.
 
Do it, you know you want to :)
It is my intention but for it to be a scientific thingy you would have to isolate the board from all sources of earth which may be impossible, you have the earthing conductor, bonds and all those circuits linked to extraneous parts like water heaters, boilers etc.. to lose. I see defeat before I start.
 
Third time I have done this, yesterday I managed the same post 13 times! I agree I assume the op means before the board not within it.
 
The experiment has taken place at a board with the earthing conductor disconnected and none of the circuits in contact with extraneous parts. With a link across the earth and neutral bars the board functions, as soon as you reintroduce the earth the rcd trips.
 

Reply to TNCS - USING NEUTRAL AS EARTH IN BOARD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
538
Fitted a remote second consumer unit to a detached annex. The supply to it was from a tncs system. The new db has been changed to a tt system for...
Replies
1
Views
784
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Today I came across an earth cable from the earth bar in the DB that went directly into the incoming neutral side of the main switch. The DB is...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock