Welchyboy1

-
Esteemed
Arms
Reaction score
986
Three phase board in mechanics shop

no main earth conductor

ZE - 586ohms

no rcd
 

Attachments

  • image.jpg
    220.3 KB · Views: 169
  • image.jpg
    231.6 KB · Views: 163
  • image.jpg
    206 KB · Views: 155
Last edited:
Havent touched it, only plugged my meggar into a socket to check zs

He wanted a price for a full eicr for his insurance.......lol!........, i said as soon as i see it, its basically a full re-wire and its dangerous, it needs urgent attention, he said he will call me.............
 
are they using any outdoor portable equipment?

Is there any socket outlets that could be expected to be used for outdoor equipment?

Check the condition of that enclosure including the security of fixing.

Check the bases of the OPDs...make sure they are OK.

What was the earthing arrangements previously?....any evidence of this?

where is the main intake?.....whats the earthing arrangements there?
 
are they using any outdoor portable equipment?

Is there any socket outlets that could be expected to be used for outdoor equipment?

Check the condition of that enclosure including the security of fixing.

Check the bases of the OPDs...make sure they are OK.

What was the earthing arrangements previously?....any evidence of this?

where is the main intake?.....whats the earthing arrangements there?

That neutral block looks a bit weird, too.
 
Havent touched it, only plugged my meggar into a socket to check zs

He wanted a price for a full eicr for his insurance.......lol!........, i said as soon as i see it, its basically a full re-wire and its dangerous, it needs urgent attention, he said he will call me.............

I hope you used the no trip function on your meter so you did not trip any RCD in circuit
 
Looks like the gland for the SWA is sitting on top of the trunking Pic 3. the person who wired it must not of known what is was for don.t see any asbestos though they look like bs88 fuses for what its worth , and i think the earthing arrangement is yet to be arranged :)
 
Looks to me as it used to be a MEM 3036 board that's been upgraded to bs88's (well for the few that's in). Needs a new board and those swa's terminating correctly, and the earth sorting, providing everything else tests out ok. Easy money!
 

Reply to Todays EICR gem - must be having one of those weeks in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
43
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
936
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock