- Reaction score
- 986
Discuss Todays EICR gem - must be having one of those weeks in the UK Electrical Forum area at ElectriciansForums.net
Full on pile of crap looks like the old asbestos fuse carriers too I hope u checked it's been removed or sealed before pulling any fuses
is it?Havent touched it, only plugged my meggar into a socket to check zs
He wanted a price for a full eicr for his insurance.......lol!........, i said as soon as i see it, its basically a full re-wire and its dangerous, it needs urgent attention, he said he will call me.............
are they using any outdoor portable equipment?
Is there any socket outlets that could be expected to be used for outdoor equipment?
Check the condition of that enclosure including the security of fixing.
Check the bases of the OPDs...make sure they are OK.
What was the earthing arrangements previously?....any evidence of this?
where is the main intake?.....whats the earthing arrangements there?
Havent touched it, only plugged my meggar into a socket to check zs
He wanted a price for a full eicr for his insurance.......lol!........, i said as soon as i see it, its basically a full re-wire and its dangerous, it needs urgent attention, he said he will call me.............
its just a phase block with no front on it.That neutral block looks a bit weird, too.
is it?
I dont throw that term around lightly but this time i believe there was no saving it
its just a phase block with no front on it.
they`v split the neutrals off at this point....
its poor ID of conductors i`ll bet is that....Yeah, three browns, though. That's interesting. Two incommers on 'red' fuse, too....must be looped.
Reply to Todays EICR gem - must be having one of those weeks in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.