1MΩ is a convenient figure dreamed up by the IET. It’s not the calculated value.

I’ll give you a scenario:
If you were to test a 50 year old 75HP 433V 3Ph motor, what would you accept for the supply cable minimum IR for L→L and L→E?

is there a RCD on the circuit? :iamwithstupid:
 
1MΩ is a convenient figure dreamed up by the IET. It’s not the calculated value.

I’ll give you a scenario:
If you were to test a 50 year old 75HP 433V 3Ph motor, what would you accept for the supply cable minimum IR for L→L and L→E?

depends on the age of the cable but i would accept a low ir figure as long as it hasnt degraded a lot from last ir test. if last ir test a year ago was say 10Mohm and this year was 1Mohm i would fail it for example

i have no idea tony
 
Last edited:
It’s a motor in a plant, no E/L protection what so ever other than OCPD.

Keep out of this tel, let the youngsters have a go.
i was being facetious, tony. whoever heard of a RCD on a motor that size. :38:
 
This is from a genuine case, a plant with 250+ motors in a damp, dusty and cold environment. The motors ranged from ½ to 800HP.

The calculation is based on a maximum of 1/10000[SUP]th[/SUP] leakage of the circuit FLC.

2 x the Ph→Ph or Ph→E DC voltage is used for the tests.
For 433V you would use 1000V DC Ph→Ph or 500V Ph→E.

I said it was a rotten question, you need the FLC from the scant information I gave.

You need to calculate the motor FLC taking in to account efficiency and power factor. It’s an old motor so 92% efficiency could be a start 0.87 PF maybe?

But we’ll base this on 75HP 92% Ef 0.87 PF where 1 HP = 764W
There could be another way though.

Anyone care to carry it on?
 
Last edited by a moderator:
There are a couple of different calculations which have been used over the years.
For complete installations there was a calculation based on the number of circuits in the installation, I'll look it up when I get home later.
The other method I know is the one Tony posted above using 1/10000th FLC as the maximum leakage.
 
It is Saturday night so I’ll leave this until tomorrow evening.

As Dave said it’s an old method but in a large installation it’s invaluable.

I said earlier, 1MΩ was a global figure adopted by the IET for ease, it has no real foundation.
 
Here we go, IR testing according to the 13th edition.

ImageUploadedByTapatalk1430004083.726987.jpg
ImageUploadedByTapatalk1430004120.369460.jpg
 
The 1/10000[SUP]th[/SUP] FLC is still relevant today on large power circuits. They would fail if the 1MΩ recommendation was applied to many installations.

Almost all of the UK’s LV distribution system would be a miserable fail but its still working.

There’s also the minor problem of just pressing the button and taking the first reading that is shown. A long cable needs a 30 second test at least, if the needle keeps rising keep your finger on the button. Every cable has a capacitive element, it needs to charge before a stable reading can be taken.

We tested a 1.7KV cable on a regular basis. At first the reports were coming back at around 5MΩ which would be in the words of the OP a tragic fail. A 5 minute test came back with 50GΩ (50,000,000,000Ω). The meter could go up to 10TΩ (10,000,000,000,000Ω).
The rule I set was if the test reached 1GΩ in 1 minute then the test was a pass, to extend the test leads to stress on the cable.

The one value for all doesn’t take different voltages in to account. 1MΩ, doesn’t fit them all.
 
Last edited by a moderator:

Reply to Tragic IR fail on EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Ok so I have been to a domestic property today, and carried out an EICR, couple of issues flagged up with regards to the usual no RCD protection...
Replies
29
Views
2K
Hello, I've recently had an EICR done on my residential let. The property is a 1-bed flat in London on the 8th floor, about 10 to 15 years old...
Replies
54
Views
29K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock