I know the subject of transporting pme from a house to an out building has been discussed many times.
This question is the DNO is only providing a single phase no earth TT supply which is fine. Want to run a sub main with swa to an out building approx 30m away. Would you only connect the the armour supply side (at the house) and only use a plastic gland outbuilding side or would you use an swa gland both ends and fit earth rods at both buildings all linked together or rods at both buildings but the earths are not connected between the two. This is small holding no other properties nearby.
 
as above. rod and earth both ends, better still is add a rod or 3 more, 1 at each end > 1m from existing .
 
Any additional rods should be outside the zone of influence of the closest rod, this means at least the length of the existing rod away from any other.
 
Any additional rods should be outside the zone of influence of the closest rod, this means at least the length of the existing rod away from any other.
Three times the length of the original rod to ensure you're outside the sphere of influence. There is a calculation for this but this is a good rule of thumb.
 
Geophagy has been considered as an adaptive behavior in humans and animals (1) and the clays have been considered the healing materials from ancient times. As geophagia is an occasionally habits of animals and humans (babies and pregnant women), physiologically it is assumed that earth might have some beneficial effects on body function. Bentonite is absorbent aluminium phyllosilicate clay. It is named after Fort Benton, Wyoming where its largest sources are found.
 

Reply to Transporting TT earthing? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
357
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
387
Morning guys, Just been to look at a CU change and there was a bit of an oddity with the PME connection in the old black cut out. Looking at the...
Replies
2
Views
656
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock